Your answer lies in the next to last line in your post. "pull a new cable."
|
|
|
Type: Posts; User: jwelectric; Keyword(s):
Your answer lies in the next to last line in your post. "pull a new cable."
You are correct about a #4
Gentlemen, there is a right way and a wrong way to do things and as pointed out many times the wrong way is not allowed on the forum.
The Department of Consumer and Regulatory Affairs for the...
Use an ammeter and be safe.
With every breaker in the panel off pick a neutral then start turning on breakers one at a time. This will tell you if the neutral shares two breakers.
...
There are several breaker manufacturers that make breakers rated for two conductors.
To use a wire nut for landing two circuits on one breaker is also acceptable.
Either method is acceptable as...
Here in lies a lot of liability for a homeowner or an electrical contractor. Safety must always come first in everything we do or we could end up in court trying to explain ourself
Not to mention...
can't go lower than the GEC
If you are having a problem reading post #11 then you should not be messing with a portable generator and the wiring of a home.
Separately Derived System. A premises wiring system whose power is...
Then it must be installed as a separately derived system as outlined in UL FTCN....
Well then your concern should be the use of the generator not the use of the box.
It is illegal to use a portable generator in the manner in which you are planning. There are several safety issues...
What do you think would be wrong with the mounting nole being on the inside. We mount many enclosures with screws on the inside such as but not limited to meter base, panel. four square boxes,...
he posted the box and here is a link to the receptacle
http://www.grainger.com/Grainger/HUBBELL-WIRING-DEVICEKELLEMS-IEC-Pin-And-1VCP6
Not sure what you are asking here, but like any other box sounds like a good answer.
As with any surge or lightning arrestor the lower the resistance to earth the more current it will dissipate in the event of a surge caused by lightning.
It is near impossible to achieve much...
Any and all ground rods must be bonded together no matter why they are installed
There is no such thing as a weather proof cord. There are weather resistant cords but after time these will fail. There is no cord that is approved to be buried under plants or the leaves of plants....
You are asking for trouble and maybe even a fire. This is a very bad idea.
Yes .
This means that are fastened in place and cord and plug is not allowed as an installation method.
Many times a Do-it-yourselfer will get a real good idea but although they think their idea is one...
Oh. I did not know that was what everyone was talking about the lights are wired to a sensor that's plugged into and outdoor socket I can unplug it and move the lights at anytime its not set in stone...
Cameron
The problem you are going to have with your own pole lights will be a battle between you and your homeowners insurance and the battle will depend on which state you live in. Nothing will...
There are several laws and codes are adopted into the law so they are laws, that come into play here. The post is being used to enclose the conductors that supply the bulb and this causes problems in...
410.6 Listing Required.
All luminaires and lampholders shall be listed.
What his means is that one cannot just throw some pipe together and call it a light. It must be evaluated by a NRTL
I just love it when the customer changes the bulbs and installs bulbs that are larger than what is called for. In such a case I charge for a service call being it was not the fault of the...
not for a bath