System is running much better... Thanks jadnashua. I bumped the low temp on the control to 180°F and left the high limit at 200°F, maintaining the 20° differential required on the warning label. Now...
|
|
|
Type: Posts; User: BLAAT!; Keyword(s):
System is running much better... Thanks jadnashua. I bumped the low temp on the control to 180°F and left the high limit at 200°F, maintaining the 20° differential required on the warning label. Now...
Okay... so I did some more research and thinking. Thanks for the suggestion of not taking things apart. I now realize that the boiler is probably adequate to heat the whole house including the...
Thanks jadnashua. How do I measure the supply and return temps? A thermocouple on the surface of each pipe, or do I need to measure the temp of the actual water flowing through by tapping the pipe...
Hi All,
I recently purchased an 1800 square foot house built in 1950 with a FHW by oil system that takes an extremely long time to get up to temperature... like 3-4 hours or more. The house has one...