Thanks, valveman. I have a setup like your picture (cycle stop valve). It works great. I have moved it to the garage. It was set temporarly at the well head during construction.
|
|
|
Type: Posts; User: lray882; Keyword(s):
Thanks, valveman. I have a setup like your picture (cycle stop valve). It works great. I have moved it to the garage. It was set temporarly at the well head during construction.
I currently have a Franklin J Class Series V Submersible Pump 1HP 15GPM 230 Volt (2 Lead Wires + Grd.) I am using 14/2 Flat Submersible Cooper Wire with ground. The pump is 190' down the well from...
Is it better to get a CSV that is adjustable? Looks like the pside kick package have one that does not. Should the poly pipe be one piece. Looks like Lowes store sales them in 100' rolls. I guess...
Valveman, what is the "1) 4 X 30 shroud (if applicable)" you are referring to?
Thanks
Thanks everyone for your comments. I forgot to tell the well water level is 50' from ground surface and the ground is level from well to proposed house. I have never used the CSV system. I do not...
Would someone give me an idea of what size submersible pump and pressure tank I need. Also, pipe size in well and to the pressure tank.
The well is 200' deep. The house will be 50' away. I plan...
Current is at the well already. I have 220 volt submersible pump in a 80 deep well currently serving another house. Are you saying run 1.25" pipe to the new house? I was wondering if a second...
If I build a house where I have choose it would be 1000' from the well and pump and an elevation difference of 40 ft up. What would I need to bring water and pressure to the new house from the...
I think it is ok. Current was not left on, but few seconds each try.
Problem solved. I did not have 230volts, but 110volts on each lead.
Thanks to all.
No low pressure switch with lever. I have the switch wired as the diagram showed. The two lead in power wires on the outside and the two wires to the pump on the inside (middle). Bare ground from...
Thanks
I did use the heat shrink at the connection near the pump. I have not found my meter, yet. Can someone tell me exactly what I am looking for and how to test with a meter? If I have two hot...
Two wire 240 volt Submersible pump, Well is 80 feet deep and 240 volts supply. Double pole Breaker (20amp) and wires are new (14ga down well). 30 amp Switch box is new at pump house. Pressure...