HJ - that is true since you have brought that up. Maybe it a combination of not enough insulation and improper ducts. The 3 ton system needs 1,200 CFM and with the 14" duct it's only 800 CFM, then...
|
|
|
Type: Posts; User: ITSec; Keyword(s):
HJ - that is true since you have brought that up. Maybe it a combination of not enough insulation and improper ducts. The 3 ton system needs 1,200 CFM and with the 14" duct it's only 800 CFM, then...
The builder's of this development used hydro heat for heat in these houses, so I do not have a heat pump or supplemental strip heaters. The 2 story houses in the development have their hot water...
I was thinking about paying for one of those online duct designs, but I'm a little skeptical about paying for that type of service. Cost is $300 and comes with materials list.
Dana - the ductless system seems like a great idea. I've been reading about HVAC systems and how they should be installed in the conditioned area and ductless seems to solve that problem since my...
Service side of air handler
http://i43.photobucket.com/albums/e397/Halstrom41/HVAC/IMG_6502.jpg
I need some advice from the experts, should I replace the duct work or the whole system?
I currently have a 3 ton Trane compressor and First Co hydro heat system installed in 2002, the house is...
Water going to the air handler is about 140F the return water I estimate 120F.
Nevermind, in my brain I thought this was a good idea. Guess I need to take off my plumber's hat and put my IT hat...
I just had an idea! I was thinking of a way to make my system more efficient since the return water from the air handler is coming back cooler. So here's my idea: I was thinking of a way to wrap...
I actually have a video of what you described, water droplets were falling onto the burner from the flue. This only happened once when I first installed the water heater, it was probably 50F outside...
Dana,
Will an aquastat help in my situation, since it's getting colder outside the air handler and water heater runs 8-9 hours a day. When the heat for the house kicks on, the air coming through...
Wow Dana, very informative; it's going to take a few times reading your post to understand but i'll get it.
Hey whatnoise I found a good website for calculating heat loss, http://www.moorepage.net/heatloss.html the website explains it very well and there is an excel spreadsheet where you can play around...
Thanks for all your help Dana! I finally have heat in the house, not fun getting ready for work when the temp in the house is 58F. From the vents I'm getting 109F, but when the shower was running...
The original water heater was rated at 65,000 BTUs, the new one is 40,000 BTUs, it should still be enough to heat the house. I did a rough calculation for heat loss and multiplied it by 1.58 and it...
Guess I purchased the wrong water heater, I assumed apollo was the only company making dual purpose water heaters. That Vertex is a sweet looking water heater but doesn't fit the budget. The water...
I had an Apollo water heater that died on me over the holiday. The Apollo water heater had 4 ports, 2 for domestic water and 2 for the air handler in the attic. I assumed the only way to heat my...
Thanksgiving day my Apollo water heater became a leaker, which meant I lost hot water and heat at the worst possible time. I was planning on replacing it summer 2012, guess it couldn't wait. I was...