ok, ill have to hold off until after my permit is satisfied..... He made a point of saying i can not send more then half my service to the garage / out building.
Thanks again guys for your help
|
|
|
Type: Posts; User: knied1; Keyword(s):
ok, ill have to hold off until after my permit is satisfied..... He made a point of saying i can not send more then half my service to the garage / out building.
Thanks again guys for your help
Next spring when i upgrade the service to my house from 100 amp to 200 amp i am planning to do that......I just needed to get power into the garage for the winter, and wanted to make sure what i was...
OK,
So over the weekend I did my install, I have one wire to each breaker on the house panel box, and one wire to each breaker in the garage panel box. From the house panel box, I have one wire...
jwelectric,
Thanks again
Just an FYI
What we do where i work is take a of pipe where the id is a little bigger than the diameter of the rod, and weld a piece of round bar to it, then if you...
OK, hopefuly this will be the last question....questions
I am looking into the grounding rods, there are both Galvanized and Copper, I am assuming that copper is the way to go. Does 5/8" or 3/4"...
jwelectric,
I MUST be missing something..... I did contact my local town building code office, They forwarded me to the Electrical Inspector / Code Enforcement officer. I told him what i am...
Homeownerinburb,
I dont understand why you are pushing this soo much. My father had 50 amps feeding his workshop, and the breaker would pop every now and then, he raised it, since i will actuially...
I did an amperage calculation, before I started looking into upgrading the electrical, Lets ignore the things like clocks, radios, cordless battery chargers, and go with the following. 5 lights at...
When i was at Home Depot last night looking into their different wires I told them that i did not want the URD, and wanted THW. There was an electrition there and he told me it was ok but only inside...
I know that immediately I am over killing it, BUT within the next few years I am going to have a mill, and lathe in the garage, before you call me out they are both single phase 220. My father is...
How far are you allowed to run URD inside a structure?
In the garage i would need to run it about 3 feet, to the panel, and in the house it would be about a 10 foot run into the panel. It seems to...
jwelectric thanks for the input but i need to hit you up again.
The wire is 4 wire aluminum, and all 4 wires are insulated individually, one has a yellow stripe. I understand that i need to be...
sorry one more question
I am told that the common and ground wires CAN be on the same bussbar in the house, BUT the ground and neutral need to be on separate bussbars in the panel. Is this true? and...
This subject may have been beaten to death, but here is my plan, and I have a couple questions.
I am running a sub panel to my garage, I have already purchased the panel box for the garage from...