  1. Replies
    5
    Views
    65

    The vent has to be downstream of the fixture, and...

    The vent has to be downstream of the fixture, and must rise vertically off the trap arm.
  2. Replies
    10
    Views
    228

    The drawing in the book would be better if they...

    The drawing in the book would be better if they had the sink teed into the vent, as it's vent would also serve as a wet vent for the water closet.

    The fittings shown are wrong as the below grade...
  3. Replies
    10
    Views
    228

    That book is well known to show things that do...

    That book is well known to show things that do not meet code in most places.
    The number one offense is that no part of a dry vent can be horizontal for any distance until it is at least 6" above...
  4. Replies
    6
    Views
    182

    There is always a potential for backflow, so the...

    There is always a potential for backflow, so the vents should be kept separate.
  5. Replies
    9
    Views
    193

    How about a photo of the trap and vent...

    How about a photo of the trap and vent installation?
  6. You would really need to have a water chemistry...

    You would really need to have a water chemistry test performed to be able to properly deal with it. There is a different forum header here on the website for water treatment issues.
  7. The sink would not drain properly. On many...

    The sink would not drain properly.

    On many vanities, you could increase the height of the toe kick and trim it out so that it looks fairly normal.
  8. Regular or braided supply hoses are not approved...

    Regular or braided supply hoses are not approved for such use, but PEX is. Personally, I would just stub up new copper after the tiling was done, and then the shut-offs can be installed under the...
  9. Replies
    4
    Views
    136

    You have to consider that the pipe must be...

    You have to consider that the pipe must be pitched no less than an inch for every 4 feet, so the chances of hiding more than part of it within the joist space is not good.
  10. If you make the trap deeper, it will not be...

    If you make the trap deeper, it will not be self-scouring and will not drain properly. Your choices are to lower the fitting in the wall or raise the vanity so the sink is higher.
  11. It looks to me like the inlet in the wall is...

    It looks to me like the inlet in the wall is about the same height as the bottom of the sink. The sanitary tee in the wall needs to be lowered on the stack. A deep sink needs the tee inlet 16-18"...
  12. Replies
    2
    Views
    94

    A professional company will use plastic sheeting...

    A professional company will use plastic sheeting to isolate the area from dust & debris. The concrete can be saw cut and removed in a square or rectangle, so that the new pour does not look like a...
  13. This is a case where the work you are having done...

    This is a case where the work you are having done legally requires a permit and inspection from your municipality. The building/plumbing inspector should be the one that is enforcing the code...
  14. I don't know where the 25psi would come into play...

    I don't know where the 25psi would come into play here, it sounds to me like bad info-- the float valve is the only control.

    A non-bladder style tank is often used to allow iron/air contact...
  15. Replies
    2
    Views
    78

    The fitting used should be a sanitary tee. You...

    The fitting used should be a sanitary tee. You can use 1/8th bends to create an offset in the vent, but the vent is not permitted to fall below 45 degrees until it is at least 42" above the floor.
  16. You have a challenge in that it might be code...

    You have a challenge in that it might be code legal, but it does not comply with the toilet manufacturer's instructions.
    There are a lot of plumbers who do not install a Toto toilet compliant...
  17. Replies
    10
    Views
    2,736

    I would trim out an access to the valves on one...

    I would trim out an access to the valves on one side of the machine.
  18. Replies
    1
    Views
    80

    You will need to open the wall up enough to get...

    You will need to open the wall up enough to get riser clamps around the stack on each level.
  19. Replies
    4
    Views
    136

    Prices can vary wildly across the country, but...

    Prices can vary wildly across the country, but here you could get a nice full bath in an existing basement for that kind of money.
    Things I would look for are any signs that the basement has...
  20. Replies
    4
    Views
    165

    It is possible that your main line has a belly or...

    It is possible that your main line has a belly or does not have enough pitch to effectively keep itself clear. Once it has been cleared, a sewer camera might be telling.
  21. Replies
    5
    Views
    132

    There is no "right way" to put anything over the...

    There is no "right way" to put anything over the top of tile in a shower. Any such method would only be an improper way to make something look better, leaving the future owner to deal with the...
  22. If your drawing is correct, each fixture needs a...

    If your drawing is correct, each fixture needs a vent. The toilet is the only fixture there that is vented.
  23. There is no sure way to know the answer as your...

    There is no sure way to know the answer as your well guy might simply not have experience with all of the possible configurations.
  24. There is no snifter. In some areas it is not...

    There is no snifter.
    In some areas it is not uncommon to install 2 bleeders in the drop pipe so that a measured amount of water can drain out. The air in this section of pipe will charge the...
  25. If the bleed hole is required it will be...

    If the bleed hole is required it will be specified in the pump installation instructions. Some pumps have it built into the discharge section of the housing.