    Since when do Electricians care about saving...

    Since when do Electricians care about saving money? :)




    Again, true, however, I always choose ampacity according to the breaker size not the appliance load.

    He, could probably get away...
  2. Replies
    11
    Views
    2,641

    True, but that's right on the border. I would...

    True, but that's right on the border. I would run #6 on a 50Amp circuit, especially if a longer run.

    KC
  3. Replies
    11
    Views
    2,641

    Well, you can't put a plug on the flex, either...

    Well, you can't put a plug on the flex, either straight blade or twist lock. You would have to replace the flex with cord.

    It should be hard wired to a box. Six feet should be enough to move the...
  4. Replies
    31
    Views
    5,543

    Correct, The Neutral/White (Grounded Conductor),...

    Correct, The Neutral/White (Grounded Conductor), and the EGC/Green (Equipment Grounding Conductor), should ONLY be bonded at the Main Panel.




    Sorry, my bad. I meant EGC [Equipment...
  5. Replies
    31
    Views
    5,543

    The grounding Electrode system is for lightning...

    The grounding Electrode system is for lightning protection not fault clearing.

    If your detached building has no metal connection to the main building, water, gas, conduit, etc, it was acceptable...
  6. Replies
    31
    Views
    5,543

    The reason that you cannot bond the Neutral to...

    The reason that you cannot bond the Neutral to the subpanel is simple. The Neutral is a Current Carrying Conductor and the Equipment Grounding Conductor, (EGC), should only carry current for fault...