Sure enough, it was a bad run cap. It was obviously bad from visual inspection alone, it was bulged and leaking. Part replaced and fan started up right away when I switched the unit on. Thanks...
|
|
|
Type: Posts; User: lohryx5; Keyword(s):
Sure enough, it was a bad run cap. It was obviously bad from visual inspection alone, it was bulged and leaking. Part replaced and fan started up right away when I switched the unit on. Thanks...
Thanks for the reply Nukeman. I've done some searching on other sites and the Run Capacitor seems to be what a lot of other people have had problems with. Unfortunately, I don't have a schematic or...
I have a Janitrol Split System Heat Pump (Goodman Manufacturing Company). The decal on the outside unit is pretty worn in some spots but I could read the following:
Model: CPJ24- (CPJ24-1AP...