Two 14's double up = how many gauge.
12 gauge or 11 gauge.
This is not for electrical.....
I'm need to buy a crimp connector sleeve and need to determine it based on a doubled up 14awg
Printable View
Two 14's double up = how many gauge.
12 gauge or 11 gauge.
This is not for electrical.....
I'm need to buy a crimp connector sleeve and need to determine it based on a doubled up 14awg
There is no cross reference. You'd have to use the tables in the back of the NEC to get the actual diameter of the conductors.
Gauge Inches (decimal) Inches (fractional) Millimeters 20 .032 approx. 1/32" .812 18 .040 > 1/32" 1.024 16 .051 < 1/16" 1.291 14 .064 approx. 1/16" 1.628 12 .081 > 1/16" 2.053 10 .102 < 1/8" 2.588 8 .128 approx. 1/8" 3.264 6 .162 > 1/8" 4.115 4 .204 < 1/4" 5.189 2 .258 approx 1/4" 6.544
Very handy chart, can you get a few more larger sizes under the 2?
How does that translate to combined. For example, I know the quad 16ag I use, the combined dual 16's = 13AWG
0 .325 5/16" 8.251 00 .365 approx. 3/8" 9.266 000 .410 7/16" 11.110 0000 .500 1/2" 12.710 9/16" .563 9/16" 14.287 5/8" .630 5/8" 15.875 3/4" .750 3/4" 19.050 7/8" .875 7/8" 22.225 1" 1.000 1" 25.400
NO.
Doubling up, does not make it *half* the wire rating.
Just don't do it often enough to know.
Found the answer - Two 14's = 11 AWG
Just making fancy speaker connections with my WBT crimp sleeves....
Don't start the bare copper vs. connector debate ;-/
I am not an engineer (thankfully), all I know is 310.4, then 310.10(H) says we CANNOT parallel conductors under 1/0.
Here is the NEC Handbook commentary on it:
310.10(H)(2) commentary:Quote:
Conductors connected in parallel, in accordance with 310.10(H), are treated by the Code as a single conductor with a total cross-sectional area of all conductors in parallel. The use of parallel conductors is a practical and cost effective means of installing large-capacity feeders or services. Using conductors larger than 1000 kcmil in raceways is neither economical nor practical unless the conductor size is governed by voltage drop. The ampacity of larger sizes would increase very little in proportion to the increase in the size of the conductor. Where the cross-sectional area of a conductor increases 50 percent (e.g., from 1000 to 1500 kcmil), a Type THW conductor ampacity increases only 80 amperes (less than 15 percent). A 100 percent increase (from 1000 to 2000 kcmil) causes an increase of only 120 amperes (approximately 2 percent). Generally, where cost is a factor, installation of two (or more) paralleled conductors per phase may be beneficial.
The parallel connection of two or more conductors in place of using one large conductor depends on compliance with 310.10(H)(2) to ensure equal current division in order to prevent overloading any of the individual paralleled conductors.
Where individual conductors are tapped from conductors in parallel, the tap connection must include all the conductors in parallel for that particular phase. Tapping into only one of the parallel conductors would result in unbalanced distribution of tap load current between parallel conductors, resulting in one of the conductors carrying more than its share of the load, which could cause overheating and conductor insulation failure. For example, if a 250-kcmil conductor is tapped from a set of two 500-kcmil conductors in parallel, the splicing device must include both 500-kcmil conductors and the single 250-kcmil tap conductor.
Quote:
To avoid excessive voltage drop and also to ensure equal division of current, it is essential that different phase conductors be located close together and that each phase conductor, grounded conductor, and the grounding conductor (if used) be grouped together in each raceway or cable. However, isolated phase installations are permitted underground where the phase conductors are run in nonmetallic raceways that are in close proximity.
The impedance of a circuit in an aluminum raceway or aluminum-sheathed cable differs from the impedance of the same circuit in a steel raceway or steel-sheathed cable; therefore, separate raceways and cables must have the same physical characteristics. Also, the same number of conductors must be used in each raceway or cable. See 300.20 regarding induced currents in metal enclosures or raceways.
All conductors of the same phase or neutral are required by 310.10(H)(2) to be of the same conductor material. For example, if 12 conductors are paralleled for a 3-phase, 4-wire, 480Y/277-volt ac circuit, 4 conductors could be installed in each of three raceways. The Code does not intend that all 12 conductors be copper or aluminum but does intend that the individual conductors in parallel for each phase, grounded conductor, and neutral be the same material, insulation type, length, and so on. Also, the three raceways are intended to have the same physical characteristics (e.g., three rigid aluminum conduits, three steel IMC conduits, three EMTs, or three nonmetallic conduits), not a mixture (e.g., two rigid aluminum conduits and one rigid steel conduit).
The presence of the word polarity throughout the section specifically allows the inclusion of dc circuits.
Since you say you hacked in a "wild mountain run" I am sure those looking to circumvent this part of the code will feel much better about themselves, as I am sure you do. :rolleyes:
Whoa. Doubling up in high voltage :eek:
The only time I've ever doubled up is with speaker wiring & when I needed to cheat and provide power to a alarm panel.
Four 24AWG (aka - cat5 cable) combined - is equivalent to 18 gauge. It was cutting it close but it was just enough gauge to make it work WITH COM working as well..
Doubled up speakers in world is my stash of QUAD 16awg and Quad 14 AWG cable....
Which I use either as a pair or quads depending on application of amplification