If you were to guess, How old would you say these fuse's are?
Not even sure what the one on the right is .... Should these be in a 5 ton heat pump rated for 50amp? They are 45amp.
Printable View
If you were to guess, How old would you say these fuse's are?
Not even sure what the one on the right is .... Should these be in a 5 ton heat pump rated for 50amp? They are 45amp.
Well, I don't think you see Gould fuses any more. I could be wrong, but I think FerrazShawmut bought up that brand.
Anyway, 45 amps could be in the ballpark for a 5 ton condenser.
So, probably more than 1 year old.
I got 24A for a 5 ton heat pump with COP = 3 at 240v. Start up current may be 6x higher.
Wrap the fuse in several layers of newspaper and hit it with a hammer. If the fuse element inside is only cracked in one place it was a fatigue failure or a mild overload. If the element is splattered it was a heavy overload.