GFCI in unfinished basement on a 220v motor load

Users who are viewing this thread

walt_pittsburgh

DIY Retired Member
Messages
5
Reaction score
0
Points
1
Location
Pittsburgh, PA
I installed a 2P standard breaker to control both a Delta 220v cabinet saw and a Jet 220v planer. I have a wall outlet in an unfinished area of the basement (my workroom) with a 220v receptacle. It then has a rather short (approx 8-10ft) heavy duty extension with the correct 220v plug and receptacle I move between these two machines. Just depends on what I am working on. Typically it stays connected to the Delta Saw. Based on NEC, is a 2P GFCI required in this application?

I have a concern that the motor characteristics may cause nuisance tripping. I noticed our furnace and an outdoor sewage pump are not connected to GFCI. I suspect it has something to do with they are both motors.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Don't take this as gospel, but I think it makes a difference if it is stationary equipment (direct wired) verses plug in. Although, in a potentially wet area, a GFCI has benefits, regardless.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
You are not the only one worried about nuisance tripping.
http://www.docstoc.com/docs/5672688...d-Fault-Equipment-Protection---Patent-7292420
The background info starts on sheet 6.

Motors have capacitance from the windings to the grounded motor shell. The current caused by this capacitance can eat up a lot of the 5 mA leakage current "budget" that GFCIs have.

You can measure leakage current and thereby infer capacitance with just a DVM, a resistor and a small fuse; you don't need a capacitance meter.

"Unfinished basement" probably means "concrete floor", and concrete is a semiconductor and not an insulator, so you probably have some cause for concern.
I guess one way around this problem while still maintaining reasonable personal safety and using a GFCI or not, is to periodically test that your equipment is properly grounded. Let's say once/month?
Are your machines double insulated?

BTW, if your breaker nuisance trips occasionally with these machines you might try using a longer and/or smaller gauge power cord as a troubleshooting aid.
 
Last edited:

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
From personal experience I have never had a GFCI false trip when I have used one on sump pumps and refrigerators and even saws.

I have had AFCIs trip though with saws.

So count yourself lucky your basement is unfinished which requires GFCI for the 120 volt circuits rather than finished which might require AFCI.

Nevertheless I do not think one is required for 220 volt circuits even in an unfinished basement. A dryer does not need one, for example. Nor does the AC unit which is outside in the rain.

I'd try the dual pole GFCI if you are worried. It will be expensive though.
 
Last edited:

walt_pittsburgh

DIY Retired Member
Messages
5
Reaction score
0
Points
1
Location
Pittsburgh, PA
Update on my GFCI Question

I installed a 2P standard breaker to control both a Delta 220v cabinet saw and a Jet 220v planer. I have a wall outlet in an unfinished area of the basement (my workroom) with a 220v receptacle. It then has a rather short (approx 8-10ft) heavy duty extension with the correct 220v plug and receptacle I move between these two machines. Just depends on what I am working on. Typically it stays connected to the Delta Saw. Based on NEC, is a 2P GFCI required in this application?

I have a concern that the motor characteristics may cause nuisance tripping. I noticed our furnace and an outdoor sewage pump are not connected to GFCI. I suspect it has something to do with they are both motors.

Thanks to those who have replied so quickly. To clarify a few points. Both machines, which weigh several hundred pounds each, are on mobile bases so they do not have direct steel contact with the concrete floor. The basement is undergound on one side (front of house) and ground level on the other (rear). I can walk out from my workroom to a patio on the back side. The workroom has a finished drop ceiling and finished drywall on one side (common to the game room). I realize the 2P GFCI will be close to $100. I am just trying to get into compliance with NEC.
 

Jim Port

Electrical Contractor
Messages
156
Reaction score
0
Points
0
Location
Maryland
Website
www.manta.com
I am not sure about some of the issues raised in post 3 above, but the UL allowance for acceptable leakage on motors is about 1/10 of the level that a GFI should trip at. You should not be having issues with sump pumps, freezers etc tripping a GFI. If you are the problem appliance needs to be repaired or replaced. The old exceptions for appliances in areas that needed GFI protection have been removed. GFI protection is now required even for the ceiling mounted receptacles in a garage. Commercial kitchens even require GFI protection for the refrigerator.
 