L7248C 1006 Honeywell aquastat

Users who are viewing this thread

stillchillin

New Member
Messages
2
Reaction score
0
Points
0
Location
Brunswick, VT
Need help! I have a Buderus boiler with a honeywell electronic aquastat. I am off grid solar with a Honda 6.5KW back up generator. The boiler works fine while inverting off the batteries, but the control locks out on a Err4 when the generator is running. I see 125V at the control while on the generator. Everything is wired properly, grounded. I have tried a few thing with no change Switched L1, L2 and additional grounding. Thanks
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
It's your generator. Generators do not always produce a clean wave and some of the new electronic controls don't like that. You can swap your boiler control out for a L8124 or L8148 which is analog and will work fine.
 

stillchillin

New Member
Messages
2
Reaction score
0
Points
0
Location
Brunswick, VT
That was my thought also, Thanks do you know of a devise to clean up the sine wave? I kind of like the control and there are boards in every appliance in the house.
 