toilet drain 3" or 4"?

Users who are viewing this thread

Zxed

Member
Messages
64
Reaction score
0
Points
6
Location
California
question about my toilet drain.... i want to know if there is any specific reason if the following is done (see image)

i can guess that the 4" allows for a smoother flush...

the current setup is for a 14" toilet rough, the new toilet is a 12"..

since i need to move it back., should i simply move it 2 inches back, or should i re-create with a 3" drain and 4" to 3" flange?
 

Attachments

  • toilet.jpg
    toilet.jpg
    6.2 KB · Views: 563

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
I'm not understanding your post.
Are you planning on having a 4" line at the toilet that then goes into a 3" line further down?
 

Iminaquagmire

DIY Senior Member
Messages
206
Reaction score
0
Points
0
Use a 3x4 reducing closet bend. It'll have a 4" inlet and a 3" outlet. Makes setting the flange much easier since you use a 4" inside fit flange. I would change it for that reason alone. That way you can leave the pipe long and tile up to it. Then when your floor is done, you can trim the pipe flush and install your flange on top of the tile for a perfect, fully supported flange. I wouldn't use any reducing couplings anywhere.
 
Last edited:

Zxed

Member
Messages
64
Reaction score
0
Points
6
Location
California
Use a 3x4 reducing closet bend. It'll have a 4" inlet and a 3" outlet. Makes setting the flange much easier since you use a 4" inside fit flange. I would change it for that reason alone. That way you can leave the pipe long and tile up to it. Then when your floor is done, you can trim the pipe flush and install your flange on top of the tile for a perfect, fully supported flange. I wouldn't use any reducing couplings anywhere.

i like the idea of triming the pipe flush after all the flooring is done..

so something like this

so once i attach the 3" to the horizontal waste drain, i will still need to drop in a 4" pipe for the top so that it sticks out high enough for me to cut flush later correct?
 
Last edited:

Zxed

Member
Messages
64
Reaction score
0
Points
6
Location
California
I'm not understanding your post.
Are you planning on having a 4" line at the toilet that then goes into a 3" line further down?

that is what is there right now. i was asking if that is fine or if i should change it 3" all the way
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
bend

For the same reason I still only do it that way. It makes a better installation, but I use the 4x3 hub and spigot bend with 6" long riser. Then I install a slip on flange that slides over the pipe and down onto the floor, and if necessary cut the riser off to fit AFTERWARDS
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
Oh your only talking about 4" right at the toilet and then 3" at the end of the bend...
Thats okay.
 

Zxed

Member
Messages
64
Reaction score
0
Points
6
Location
California
For the same reason I still only do it that way. It makes a better installation, but I use the 4x3 hub and spigot bend with 6" long riser. Then I install a slip on flange that slides over the pipe and down onto the floor, and if necessary cut the riser off to fit AFTERWARDS

Thankyou all.