How to diagnose Ultramax flushing problem?

Users who are viewing this thread

JCH

Member
Messages
248
Reaction score
0
Points
16
Location
Victoria, British Columbia, Canada
Installed a Toto Ultramax in our ground floor bathroom last year. Works flawlessly. Never blocks.

Was having problems with the old (medium-flow) 9L/flush Crane toilet upstairs (frequent blockages). Snaked the line. Didn't make any difference. This toilet has always had flushing issues.

Finally bought a second Ultramax and installed it upstairs, replacing the old Crane.

This upstairs Ultramax now blocks after every BM. Liquid flushing--no problem. Solid flushing -- makes a gurgling sound, doesn't flush completely, then doesn't flush at all on the next attempt. Needs a plunger to unplug it. Blocks on next BM.

The snake is coming up clear.

1) How do I diagnose what the problem is?

2) Could it be that there is no (or reverse) slope on the toilet's drain pipe (looks approx 8 feet from stack)? If so, how would I diagnose this without ripping down the ceiling below the toilet? (I'm thinking that the lower flow Ultramax would probably make such a problem worse).

3) Is it likely to be an obstruction in the drain pipe that a snake won't "find" or clear?

Help!
.../j
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
Two toilets plug on the same line?
Sounds like the line.
I would pull the toilet up and get someone in with a large snake for the waste line, the kind for main lines.

You can then test the toilet on blocks outside and make sure it's not the trapway of the bowl just to be sure.

When we set toilets, we always set the wax on the flange, and then drop the toilet onto the wax.
A wax ring can fall off and drop over the drain opening otherwise.
 

JCH

Member
Messages
248
Reaction score
0
Points
16
Location
Victoria, British Columbia, Canada
Terry said:
Two toilets plug on the same line?
Sounds like the line.
That's what I thought too.

Terry said:
I would pull the toilet up and get someone in with a large snake for the waste line, the kind for main lines.
Okay thanks--my snake is just a dinky residential one.

How would you determine whether the line is not sloped (or vented) properly without ripping open the ceilings below? Like I said, this has been a chronic problem, although more prevalent recently (which to me would suggest a plug, and possibly bad line installation too).

The old (medium-flow) toilet blocked a couple of times per month. The (low-flow) Ultramax plugs on *every* BM. It's as if there's a hump in the drain line that the low-flow can't make it over. But I'm just guessing.

Would you use a camera??

Terry said:
You can then test the toilet on blocks outside and make sure it's not the trapway of the bowl just to be sure.
This happened starting on the *first* day of the new Ultramax. Oh man, I'd like to hope that it wasn't pre-plugged from the factory...:)

Terry said:
When we set toilets, we always set the wax on the flange, and then drop the toilet onto the wax.
That's what I did. Even used a reinforced wax ring with a plastic horn.

Would a camera be overkill?

.../j
 
Last edited:

Markts30

Commercial Plumber
Messages
625
Reaction score
1
Points
0
Location
Phoenix, AZ
A camera certainly would not be my first choice here...
When you remove the WC you should be able to see into the closet bend...
If there is any liquid there, there is back-grade (or a clog)...
The pipe should be fairly clean (no obvious waste) and empty of free liquids...
I would then pour a bucket of water into the pipe and see what happens...
If the water does not flow down the pipe as fast as you can pour it (should NOT overflow) , you have a problem that may require a plumber...
 
Last edited:

JCH

Member
Messages
248
Reaction score
0
Points
16
Location
Victoria, British Columbia, Canada
Terry said:
Well, I've never heard of a pre-plugged toilet, so I would think it's the line.

Roto Rooter
How would I distinguish between:
- a properly sloped/vented line that is plugged (and therefore works well immediately after being roto-rooted)? and
- a line that is not sloped/vented properly and will therefore continue to be on the verge of plugging? (i.e. will need repeat calls)

Is there a way to tell on the first call?

Thanks!
.../j
 

JCH

Member
Messages
248
Reaction score
0
Points
16
Location
Victoria, British Columbia, Canada
markts30 said:
A camera certainly would not be my first choice here...
Okay.
markts30 said:
When you remove the WC you should be able to see into the closet bend...
If there is any liquid there, there is back-grade (or a clog)...
The pipe should be fairly clean (no obvious waste) and empty of free liquids...
I did this before installing the Ultramax. No liquid. Pipe clean. At the time I thought for sure that this meant the old toilet was the culprit.
markts30 said:
I would then pour a bucket of water into the pipe and see what happens...
If the water does not flow down the pipe as fast as you can pour it (should NOT overflow) , you have a problem that may require a plumber...
Again, when installing the Ultramax, I first poured a gallon of water into the open pipe from a jug, and it disappeared as quickly as I could pour it. Perhaps I needed more than 1 gallon of water? Or I needed a bucket that I could pour more quickly? (although any faster and it would probably spill all over the floor).

One thing that might be relevant is that a vent pipe from this bathroom comes out into the side attic *under* the floor (i.e. the vent comes along between the floor joists and then up and through the roof). Isn't a vent supposed to be *above* the highest water line in any fixture?

There's a sink and tub in that bathroom too. The stack is right behind the sink, which is between the tub and the toilet. The tub drains very quickly.

Thoughts?
.../j
 

JCH

Member
Messages
248
Reaction score
0
Points
16
Location
Victoria, British Columbia, Canada
Another thought.

Maybe they used a 90-degree bend in the waste line? When I looked in the toilet bend I saw that it was heading off parallel to the floor joists, but the stack is about 5 feet (4 joist bays) over.

The wiring in this upstairs bathroom was done by a DIY--not sure whether the plumbing was too...

.../j
 

TPA

Member
Messages
39
Reaction score
0
Points
6
Location
Florida
1 gallon isn't much water when you think about it -- the flush alone is 1.6. If you've got a 5 gallon bucket, try mostly filling it with water and dumping it down the toilet. It should be able to take the whole 5 gallons without a problem.
 

JCH

Member
Messages
248
Reaction score
0
Points
16
Location
Victoria, British Columbia, Canada
TPA said:
1 gallon isn't much water when you think about it -- the flush alone is 1.6. If you've got a 5 gallon bucket, try mostly filling it with water and dumping it down the toilet. It should be able to take the whole 5 gallons without a problem.
Just tried it with a 10-gallon bucket. No problems...

Except, afterwards the bathtub drain started making gurgling noises.

Which, to me, suggests a venting problem.

Maybe it is linked to the vent that comes out from within the joist bay.... Perhaps the vent connection is too low, and is plugging up with *ahem*.

Another thing that makes me suspicious of the venting is that the vent pipe comes out into the side attic via the joist bay (a 6+ foot horizontal run), runs up the 3 foot pony wall, about 20 feet along the top of the pony wall, then disappears up between the bedroom ceiling and the roof sheathing, where it finally goes through the roof. It's as if they cut the roof vent hole 6 feet from the *front* of the house, rather than 6 feet from the *back* of the house and decided to run 20 feet of tubing to connect it up anyway.

Would bad venting explain this behaviour?

.../j
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
Sounds like bad venting.

Is this an older home with cast iron and galvanized DWV?

Do you have trees overhanging where the vent exits the roof?

If you can get on the roof with a flashlight you can look into the vent for any build up of debris in the vent from outside sources. I have seen all kind of stuff like leaves, branches, dead animals, ect.
 
Last edited:

JCH

Member
Messages
248
Reaction score
0
Points
16
Location
Victoria, British Columbia, Canada
Cass said:
Sounds like bad venting.

Is this an older home with cast iron and galvanized DWV?
Cast iron only in the basement. The rest of the house has been switched over to ABS. The second story (actually 1/2 story) where the problematic toilet is was converted from attic space in 1992 so that plumbing is all comparatively new.

In the four years that we've lived here, its flushing has always been so-so (see my first post), but now with this new low-flow Ultramax, it's horrible. Perhaps it's because the Ultramax shoots water into the drain a lot faster than the old siphon-style toilet?

Cass said:
Do you have trees overhanging where the vent exits the roof?
No trees that tall on the property.

Cass said:
If you can get on the roof with a flashlight you can look into the vent for any build up of debris in the vent from outside sources. I have seen all kind of stuff like leaves, branches, dead animals, ect.
Oh my. The vent immediately takes a 45-degree bend and follows along under the roof surface so I won't be able to see very far (see post #10 for gory details on the 40 foot circuitous path that the vent takes).

Arrrrgh...

.../j
 