radiator supply line

Users who are viewing this thread

Steve39

New Member
Messages
3
Reaction score
0
Points
0
I have a gas fired boiler with hot water radiators. During a previous renovation I had radiator lines (supply and return) run into a room that was without a radiator. The pipes were stubbed in and individually capped. Now that I am renovating this room I have opted to to forgo installing a radiator as I am installing electric baseboard heat. My question is this: before I close in the wall where these pipes are located should I make a loop between the two lines or can I leave them individually capped? Thanks in advance for any help.
Steve
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
radiator

It depends on the system. If it is a "MonoFlow" type diversion tee system you should tie the two together so the maximum water is available, or remove that tee, or tees depending on whether they used one or two MonoFlo tees, from the system.
 

Steve39

New Member
Messages
3
Reaction score
0
Points
0
resolution

HJ
Wouldnt it be the safest bet to sweat the two together as I havent a clue if it is "monoflow" and any tees that exist are buried in a wall.
steve
 