Toilet supply with built in shutoff

Users who are viewing this thread

Peanut9199

Customer Service Manager Plumbing Wholesale
Messages
869
Reaction score
2
Points
0
Location
Ontario, Canada
I've had somes calls and wanted to share.

Home Depot and maybe some other places are selling a Watts (Floodsafe) S/S toilet supply that has a built in shutoff that if the toilet leaks it will shut off the water.

The problem is it affects the Toto toilet and will not supply water to the fill valve.
I'm not sure why but it must sense a loss in pressure and stops.
So if you get a call with a fill valve not supplying any water check the supply tube.
http://www.watts.com/pro/whatsnew/whatsnew_floodsafe.asp
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
That problem is well documented and occurs on many fixtures and appliances when Watts Floodsafe supplies are installed.

IMHO they are Junk!
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
Watts Floodsafe toilet supply

I first reported that problem in September 2006
You can't use a Watts Floodsafe supply on a Toto.
https://terrylove.com/forums/showthread.php?t=8640&highlight=floodsafe

attachment.php
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Floodsafe

FLoodsafes think any high flow is a rupture and shut off. When you turn on the control valves you have to do it gradually or they will activate and then you must turn off the valve and remove the Floodsafe to reset it and then try again.
 

SteveW

DIY Senior Member
Messages
1,282
Reaction score
22
Points
38
Location
Omaha, NE
They have washing machine hoses with the same valve. Same problem with false alarms.
 

Redwood

Master Plumber
Messages
7,335
Reaction score
13
Points
0
Location
Connecticut
I had a go round with a condo association regarding them requiring the use of floodsafe washing machine hoses...
They had 100 PSI. water pressure, yet wouldn't have a PRV installed, and they were requiring floodsafe washing machine hoses...

Somehow it just wasn't working...
Go figure!
 