Updating Kitchen wiring in a 60 year old house

Users who are viewing this thread

Ron1111

Not a Licensed Professional
Messages
17
Reaction score
0
Points
1
Location
South Texas
What is the recommend size for the Ground wire in a 50A circuit? Everything is Copper wire. Of Course all the old wiring is pre ground with two prong outlets. Fortunately everything was run in FMC and hopefully I can pull new wire. The stove is also 3 prong with #6 in what looks like either 3/4 or 1" FMC. It will updated to 4 wire as well.
 
Last edited:

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
So is that the general rule of thumb? Example: three #2 and a #6 ground.
No as it is usually based on your breaker size. From NEC - Table 250.122

706ecmCBtable1.jpg
 
Top