Side Split Cantilever Insulation

Users who are viewing this thread

Dennis Wilson

New Member
Messages
1
Reaction score
0
Points
1
Location
Ontario, Canada
Hi everyone,

I'm having my soffits/siding/eaves done in the near future, so I thought it was a good time to address the freezing cold room above the cantilever on my 60s 4 level side split.

After taking everything out, how would you guys best approach insulating this area? I also want to add two pot lights into the cavity. I see that there is no blocking between the garage side and the cantilever side. Also seems to be a gap above the door that leads to more insulation running in the ceiling in the entry way.

Entry Way
front house view.JPG

Above Door
over door.JPG


Right side to garage
right side to garage.JPG
 

Attachments

  • full view.JPG
    full view.JPG
    82.8 KB · Views: 195

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Before insulating the framed floor seal the foundation sill to the foundation and build air dams to prevent even the slightest convective air (= air transported moisture) between the conditioned indoor air space and the cantilever insulation cavity. It looks like you will need to pull some pre-existing batts to be able to get a good seal on the air dam on one side, on the other you can just use polyurethane caulk to seal the band joist to the ship-lap subfloor, taking care that the bead of caulk fills in between planks rather than skipping over them.

The odds are pretty good that there is rosin paper or other similar reasonably air tight underlayment between the subfloor and finish layers above (?). If not, what is the finish floor type, and what sort of underlayment (if any). I If the floor is inherently air leaky it's better to install a layer of rigid foam board (any type, any thickness) tight to the subfloor and seal it completely to the joists and the air barrier over the foundation, as in this detail:

index.php


The air barrier over the foundation need not be foam board- MDF or OSB would do just fine- it's vapor permeance doesn't much matter as long as it's air tight. Ideally there would be foam or fiber insulation that extended all the way to the interior side. At the band joist area is it insulated on the interior?

The gap over the door header looks alike a PITA to insulate, and it may be worthwhile to fill it with 2-part closed cell polyurethane foam. The smallest ( 12-15 board foot) FrothPak or Touch'n'Seal would be enough, might be just the ticket for sealing & insulating that part, and may prove useful for sealing up larger gaps elsewhere. Closed cell foam has a fairly hefty environmental footprint when blown with HFC2245fa (as all DIY kits are), which is an extremely powerful greenhouse gas, but for making reliably air tight insulation in messier retrofit applications there's still a good rationale for using it.

Fill the cantilever framing COMPLETLY, with whatever fiber is cheap and available. Rock wool is great from a high R/inch and fire control point of view, but blown cellulose is far more air retardent, and is also "greener", if you have cheap/free access to an insulation blower. If batts, cut some thin batts out of the full thickness batts to make well fitting triangles at your bracing in the joist, and make sure there are no compressions or voids be for sealing it all in. A purpose-made batt knife isn't very expensive, but a 9"-10" bread knife works nearly as well in a pinch.

The bottom is best clad with something fairly moisture permeable such as MDF or asphalted fiberboard or exterior grade fiberglass clad gypsum board, but CDX is fine too. If the joists are smaller than 2x10 or in your local area the local wintertime temps dwell below -25C regularly it might be worth installing cut up edge strips of 1.5" EPS foam board as a thermal break on the framing, which also allows 1.5" more fiber insulation. In most of southern Ontario the thermal break foam strips wouldn't necessarily be worth it, but in northern and western Ontario it will provide a noticeable difference in barefoot comfort over the cantilever.
 

khabuda

New Member
Messages
1
Reaction score
0
Points
0
Location
Fort Collins, Colorado
Before insulating the framed floor seal the foundation sill to the foundation and build air dams to prevent even the slightest convective air (= air transported moisture) between the conditioned indoor air space and the cantilever insulation cavity. It looks like you will need to pull some pre-existing batts to be able to get a good seal on the air dam on one side, on the other you can just use polyurethane caulk to seal the band joist to the ship-lap subfloor, taking care that the bead of caulk fills in between planks rather than skipping over them.

The odds are pretty good that there is rosin paper or other similar reasonably air tight underlayment between the subfloor and finish layers above (?). If not, what is the finish floor type, and what sort of underlayment (if any). I If the floor is inherently air leaky it's better to install a layer of rigid foam board (any type, any thickness) tight to the subfloor and seal it completely to the joists and the air barrier over the foundation, as in this detail:

index.php


The air barrier over the foundation need not be foam board- MDF or OSB would do just fine- it's vapor permeance doesn't much matter as long as it's air tight. Ideally there would be foam or fiber insulation that extended all the way to the interior side. At the band joist area is it insulated on the interior?

The gap over the door header looks alike a PITA to insulate, and it may be worthwhile to fill it with 2-part closed cell polyurethane foam. The smallest ( 12-15 board foot) FrothPak or Touch'n'Seal would be enough, might be just the ticket for sealing & insulating that part, and may prove useful for sealing up larger gaps elsewhere. Closed cell foam has a fairly hefty environmental footprint when blown with HFC2245fa (as all DIY kits are), which is an extremely powerful greenhouse gas, but for making reliably air tight insulation in messier retrofit applications there's still a good rationale for using it.

Fill the cantilever framing COMPLETLY, with whatever fiber is cheap and available. Rock wool is great from a high R/inch and fire control point of view, but blown cellulose is far more air retardent, and is also "greener", if you have cheap/free access to an insulation blower. If batts, cut some thin batts out of the full thickness batts to make well fitting triangles at your bracing in the joist, and make sure there are no compressions or voids be for sealing it all in. A purpose-made batt knife isn't very expensive, but a 9"-10" bread knife works nearly as well in a pinch.

The bottom is best clad with something fairly moisture permeable such as MDF or asphalted fiberboard or exterior grade fiberglass clad gypsum board, but CDX is fine too. If the joists are smaller than 2x10 or in your local area the local wintertime temps dwell below -25C regularly it might be worth installing cut up edge strips of 1.5" EPS foam board as a thermal break on the framing, which also allows 1.5" more fiber insulation. In most of southern Ontario the thermal break foam strips wouldn't necessarily be worth it, but in northern and western Ontario it will provide a noticeable difference in barefoot comfort over the cantilever.
I have been searching for clarification on a situation just like this, so I'm sorry for reviving a dead thread. In your diagram above, you have the blocker placed over the brick wall. I have the same design under my cantilever, and the air gap between the brick and the sheathing has been venting into the joist bay since 1967. There has been zero insulation in that space the whole time. I am in the middle of this insulation project, and what I decided to do is definitely a compromise in my book. I did just like you diagramed above, and left the air gap on the conditioned side. I realize that logically, this could result in moisture issues, but that is the way it was built initially, and I don't have any evidence of moisture issues so far. I also realize that I am screwing myself out of the maximum gain from insulating the cantilever since there is still air exchange going on into the conditioned space. I am in Colorado, so it is very dry here and I'm guessing that is why there hasn't been a more pronounced moisture issue with this design.

I feel like probably the absolute best version of this insulation job would be to push the blocking into the joist cavity, so that the air gap is inside of the new insulation, foam the air gap, and then drill in new ventilation holes in the brick veneer so that the air exchange is all exterior of the framing. Can anyone confirm if 1. My leaving the air gap inside of the conditioned space (knowing that this is the way it always was) is super stupid other than continuing to compromise the insulation situation. And 2, if my proposal to change the wall vent location to somewhere on the face of the wall is a good idea.
 