Did not closely follow the latest string of posts, but a few points:
- The shower requires a 2" trap and trap arm. The tub can be 1-1/2" or 2", there's something to be said for 2". The horizontal drain from vent location to drain location must be 2".
- Both trap arms could hit a 2x2x2x2 san-tee with sanitary side inlet, not sure if that's available in ABS. Or you could use a 2" double fixture fitting.
- Otherwise, you could use vertical wet venting by having the tub trap arm hit an upper (possibly street) san-tee, and the shower trap arm hit a lower san-tee. Oddly, the reverse order is not allowed by the UPC with a 2" wet vent.
- Or you could use horizontal wet venting by having either fixture hit a san-tee, and the other fixture hit the horizontal pipe drain from the vent location to the drain location.
Cheers, Wayne