Here is the way the state says water wells should be sealed. Sometimes you can't get 10' of cement down when doing rehab on and old well, but we always tried to get it as deep as possible. Then the slab over the well has to be a full 2' on all sides of the casing and sloped from the center.
(e) Annular Seal. The annular space to a minimum of ten (10) feet shall be three (3) inches larger in diameter than the casing and filled from ground level to a depth of not less than ten (10) feet below the land surface or well head with cement slurry, bentonite grout, or eight (8) feet solid column of granular sodium bentonite topped with a two (2) foot cement atmospheric barrier, except in the case of monitoring, dewatering, piezometer, and recovery wells when the water to be monitored, recovered, or dewatered is located at a more shallow depth. In that situation, the cement slurry, or bentonite column shall only extend down to the level immediately above the monitoring, recovery or dewatering level.
(f) Surface Completion
(1) In all wells where plastic casing is used, except when a steel or polyvinyl chloride (PVC) sleeve or pitless adapter, as described in subsection (g) is used, a concrete slab or sealing block shall be placed above the cement slurry around the well at the ground surface.
(2) The slab or block shall extend laterally at least two (2) feet from the well in all directions and have a minimum thickness of four (4) inches and should be separated from the well casing by a plastic or mastic coating or sleeve to prevent bonding of the slab to the casing.
(3) The surface of the slab shall be sloped to drain away from the well.
(4) The top of the casing shall extend a minimum of twelve (12) inches above the land surface except in the case of monitoring wells when it is impractical or unreasonable to extend the casing above the ground.
https://www.tdlr.texas.gov/wwd/wwdrules.htm#76103