Cold showers after new water heater install.

Users who are viewing this thread

Shoestring

New Member
Messages
5
Reaction score
0
Points
1
Location
IL
(New install) Bradford White 50-gallon atmospheric vent. Since install water at several locations is only around 110 F. (including shower near water heater). Water also fluctuates between 110 - 135 at times. Even on very high setting this is the case. There is a small sink near the tank that is supplied by a 1/2'' copper line from a "T" off the 3/4'' copper right above tank. For some reason this faucet is at 165F, while a shower close by supplied by the 3/4'' is 110F. Any advice would be appreciated. No problem before the new water heater was installed.
 

Shoestring

New Member
Messages
5
Reaction score
0
Points
1
Location
IL
Thanks for the reply! This is happening at more than one faucet. Is it possible for debris to be an issue after a water heater change out?
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,540
Reaction score
358
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
If they are single-handle bath and shower faucets it will probably be the cartridges that need changing out..
if it is going on in common 2 handle lavatory faucets you have more of a mystery on your hands.....

most likely a bunch of junk went up the lines and is stuck in the faucets... if they are Delta or Moen it will be
easy to find the parts..... if they are some off brand like Tuscany or Price fister you are screwed
 

Sylvan

Still learning
Messages
2,767
Reaction score
696
Points
113
Location
New York
Install a 27" heat sink on the CW line prior to connecting to the tank to prevent stratification of cold mixing with the hot .

This usually corrects erratic temperature fluctuations
 

John Gayewski

In the Trades
Messages
4,384
Reaction score
1,360
Points
113
Location
Iowa
Is this a recirc system? It sounds like there a cross connection between the hot and cold somewhere which is what Mark is eluding to.
 

Shoestring

New Member
Messages
5
Reaction score
0
Points
1
Location
IL
Dual handle faucets upstairs at 130F. Single handle shower 100F. The thing is the water heater is on max temp and that sink in the basement tapped of the 3/4'' on top of the WH is at 165F. No recirc system.
 

Shoestring

New Member
Messages
5
Reaction score
0
Points
1
Location
IL
Hey guys thanks for all the great replies! I really appreciate all your help! I have some new information. After shutting off the cold water supply to the tank and draining off about 5 to 10 gallons the tank is quickly refilled by cold water entering through the hot side. It refills Within a couple of minutes. I am assuming one of the faucets is bad causing this to happen. What is the correct troubleshooting procedure. What about bath and shower faucets where I'm unable to shut off their supply?
 

Reach4

Well-Known Member
Messages
38,940
Reaction score
4,452
Points
113
Location
IL
Do you have a two faucet sink in the basement where you have connected the two with a mixer hose?

everbilt-washing-machine-parts-hrbfil02eb-64_100.jpg


Start there.

If you have nothing like that, turn off the supply to the WH. Run hot water, perhaps out of the WH drain. As the crossover passes water. At some place you may hear flow, feel flow, or feel the cold that the flow of cold water makes.

You could use an IR thermometer to measure metal supply line or valve temperatures, or use your hand to feel.
 