Changing hot water heater, 3800 to 4500

Users who are viewing this thread

Danny Brown

New Member
Messages
1
Reaction score
0
Points
1
Location
San saba tx
Im haveing to change from a 50 gal 3800 watt to a 40 gal 4500 watt do i need to change the breaker from 20 amp
 

LLigetfa

DIYer, not in the trades
Messages
7,508
Reaction score
581
Points
113
Location
NW Ontario, Canada
Using basic math, 4500W at 240V is less than 20A but what is the code req in your area? Code may req 125% of the heater's rated ampacity. What does the water heater manufacturer say? What is the wire size? The breaker cannot be increased if the wire size is inadequate.
 

hj

Master Plumber
Messages
33,604
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Wire size is the limiting factor. If you have #12, you CANNOT use a larger breaker, even though 4500 elements usually have a 30 amp breaker. WHY are you going to a 40 gallon heater in the first place, regardless of the element sizes?
 

WorthFlorida

Clinical Trail 5th session completed 4/24/24.
Messages
5,769
Solutions
1
Reaction score
1,000
Points
113
Location
Orlando, Florida
You can buy 3800 watt elements to replace the 4500 watt units. This is commonly done when the electric is NOT 10 gauge wire with 30 amp breaker. If it is 12 gauge and 20 amp you are limited to 3800 watt elements.

When I worked at Sears during the 1990’s, Sears probably sold more replacement water heaters than anyone. Since they had to cover the entire market, millions of homes were built with 20 amp, 12 gauge wire. For liability protection and not telling customers they needed to upgrade the electric, the 3800 watt unit was almost standard for them. Nowadays with Home Depot and Lowe’s, there is no product training so a lot of 4500 watt units get installed by the DIYer that should not be.

A 4500 watt element uses 18-19 amps. A 20 amp breaker may or may not trip but continuous use the breaker will degrade and the wires may run warm at the connections. The insulation may slowly degrade and get false tripping at the breaker because breakers trip on heat. For a friend who had a problem with the water heater, it turned out the pervious owner rewired the water heater so both elements were on at the same time ( a big no no). Amazing the house didn’t burn down with 12 gauge wire and the breaker internally had fused where it could not trip. It started to trip after a home inspector switched off and on all breakers, then the water heater was tripping all the time. A very short distance from the circuit breaker to the water heater is what might have saved the day.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks