Can a 1/4 bend be used at the bottom of a plumbing stack?

Users who are viewing this thread

DIYNero

New Member
Messages
14
Reaction score
0
Points
1
Location
dc
I am very limited on space and trying to figure out what would work. The line will then travel about 8 feet and then turn vertical, then back horizontal to connect into a wye combination. happy to answer any questions.
 

Tuttles Revenge

In the Trades
Messages
4,205
Reaction score
1,460
Points
113
Short answer is No.

Transitions in direction of flow from vertical to horizontal must be done with a long sweep fitting.

Pipe that is at a 45° can be considered both or either vertical or horizontal. Can that configuration help lower the height of a long sweep fitting?
 

DIYNero

New Member
Messages
14
Reaction score
0
Points
1
Location
dc
Short answer is No.

Transitions in direction of flow from vertical to horizontal must be done with a long sweep fitting.

Pipe that is at a 45° can be considered both or either vertical or horizontal. Can that configuration help lower the height of a long sweep fitting?
ah, do you mean like two 45's to cope the angle?
 

Tuttles Revenge

In the Trades
Messages
4,205
Reaction score
1,460
Points
113
ah, do you mean like two 45's to cope the angle?
No. I mean that if your stack is coming down at a 45° angle from plumb out of your slab into the wall, the overall height of the top of the fitting is lower than if it were standing up at 90°.

\ or / vs |
 