  1. Jimmy38

    PTAC Unit E1 (Freeze Protection) Keeps Kicking On

    Thanks, I've unclipped the thermistor from the coil. I just tested it in the room and then in ice water so I now have a good range of resistance values: 85 degrees: 5.95K Ohms 70 degrees: 9.38K Ohms 60 degrees: 11.2K Ohms 32 degrees: 19.75K Ohms I'm still waiting on the manufacturer to give me...
  2. Jimmy38

    PTAC Unit E1 (Freeze Protection) Keeps Kicking On

    Thanks for the reply. I'd cleaned the filter but get the same error. I also unplugged the sensor from the control board but I get a new error code and it won't run. I've attached a picture of the wiring diagram but will try to take a better one. The coil itself was room temperature and still...
  3. Jimmy38

    PTAC Unit E1 (Freeze Protection) Keeps Kicking On

    Hi All, I have two Simon-Aire model SSK818H-TP's that were installed about 5 years ago. Last year, the condenser fan blades broke in both units around the same time, so I had them replaced. Since the blades were replaced, in cool mode, the compressors in both units will kick on for a few...