Hi, Installed and wired hot water heat when I flipped the breaker it blew, After disconnecting the wires from the heater I flipped the breaker on and it worked fine and the wires tested fine, I'm using a basic double poll 30 amp square D breaker I bought from home depot, Is there a certain type of breaker I should be using. Thanks
 

Reach4

Well-Known Member
Messages
38,796
Reaction score
4,412
Points
113
Location
IL
It seems likely that you either have a short to ground , or you have a wire to wire short circuit in the water heater. I would turn off the power and troubleshoot with an ohmmeter.

With the wires disconnected from the heater, I would measure the resistance of either heater wire to a metal pipe on the water heater or another good ground that is not part of the electrical system. Each should be something over 1 megOhm normally, and it would be something less than 10 Ohms to blow the breaker. The same applies to the terminals on the water heater.

A wire to-wire-short would be a bit harder to detect. I would expect the resistance between the disconnected hot wires of the water heater to be more than 40 ohms for each isolated element, and more than 20 ohms if there are two elements.

Assuming you track the problem to the water heater, with ohmmeter readings in hand, I would try phoning the manufacturer or seller.
 

MACPLUMB

In the Trades
Messages
1,080
Reaction score
83
Points
48
Location
HOUSTON, TEXAS
It's simple he dry fired the upper element by not totally filling with water first, hince a direct short
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
An inexpensive multimeter (under $10, often free with any purchase at one tool chain) is a good investment for the home troubleshooter.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; An inexpensive multimeter (under $10, often free with any purchase at one tool chain) is a good investment for the home troubleshooter.

And a good way to get electrocuted if you do NOT know how to use it, regardless of what it cost.
 