Hi everyone,
I am planning on converting the bathroom vanity to a double sink during our bathroom remodel.
Mu question is regarding the setup I have in mind.
This is what I have
current.png

I am planning on cutting into the pipe above and below the trap arm indicated by the red line (shown below). Pipes are 1.5 steel. Now would it be ok to use a double sanitary tee or should i use a double wye (marked as 1)
proposed.png


I am planning on using two 45s on the bends to the trap adaptors on each run (indicated by 2 and 3).
Last, pipe goes between the studs and I dont want to cut into them. I am planning on offsetting them and bringing them by usinc the 45s so they come out of the studs bays and into the open space. Is this a reasonable design?
20230320_124838.jpg
 
Last edited:

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
Minnesota uses the UPC, so your horizontal 1.5" drain to the stack is limited to one sink. For two sinks, you'll need to upsize the drain to 2" all the way to the stack.

Cheers, Wayne
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
@wwhitney Thanks a lot for mentioning this. I totally forgot about that...
So the steel vent pipe is 2 inches and it goes down to 1.5 inch. The drain itself is 1.5.
What they did originally back in the 50s was to join steel with some lead pipes of the same size. I traced the lead pipe and it goes into a 2 inch cast iron pipe. I can cut down right after the hub and put a banded shield and go to ABS/PVC. Assuming I correct the vent and drain line size, is the setup I have correct? And I assume a sanitary tee for two drain lines going to a vertial pipe is correct, or do I need a double wye?
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
I traced the lead pipe and it goes into a 2 inch cast iron pipe. I can cut down right after the hub and put a banded shield and go to ABS/PVC.
Sure. [Where you say "lead pipe" I assume you mean galvanized.] Or you can remove the galvanized from the hub and get a rubber donut to join new 2" ABS into the hub. But as the galvanized is presumably leaded into the cast iron hub, your idea is probably simpler.
Assuming I correct the vent and drain line size, is the setup I have correct? And I assume a sanitary tee for two drain lines going to a vertial pipe is correct, or do I need a double wye?
I didn't really follow your description of the arrows at 2 and 3. But just looking at your drawing as an elevation, at the crossing point you want to use a 2x1.5x1.5x1.5 double fixture fitting. That's a fitting shape that is intermediate between a double sanitary tee and a double wye. The top of the fitting profile is like the double sanitary tee, which you need for venting the two trap arms, and the bottom of the fitting profile is closer to a double wye, which helps with the drainage.

If you have trouble finding the 2x1.5x1.5x1.5 fitting, you could use a 2" fitting with 2x1.5 reducer bushing. And of course the vent can be 2" if that's simpler, but only a 1.5" vent is required.

If you use the double fixture fitting, and then follow the normal rules for trap arms, the installation shown complies with the UPC. I hear it can be hard to snake through a double fixture fitting rather than skipping across, so adding a cleanout below the double fixture fitting could be useful in the future.

Cheers, Wayne
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
Sure. [Where you say "lead pipe" I assume you mean galvanized.] Or you can remove the galvanized from the hub and get a rubber donut to join new 2" ABS into the hub. But as the galvanized is presumably leaded into the cast iron hub, your idea is probably simpler.

I didn't really follow your description of the arrows at 2 and 3. But just looking at your drawing as an elevation, at the crossing point you want to use a 2x1.5x1.5x1.5 double fixture fitting. That's a fitting shape that is intermediate between a double sanitary tee and a double wye. The top of the fitting profile is like the double sanitary tee, which you need for venting the two trap arms, and the bottom of the fitting profile is closer to a double wye, which helps with the drainage.

If you have trouble finding the 2x1.5x1.5x1.5 fitting, you could use a 2" fitting with 2x1.5 reducer bushing. And of course the vent can be 2" if that's simpler, but only a 1.5" vent is required.

If you use the double fixture fitting, and then follow the normal rules for trap arms, the installation shown complies with the UPC. I hear it can be hard to snake through a double fixture fitting rather than skipping across, so adding a cleanout below the double fixture fitting could be useful in the future.

Cheers, Wayne
Thanks! So the 'lead pipe' I mentioned is like a steel pipe but it has been bent to conform to the turns they needed. Unlike the steel pipe, it is continuous and is one run from the trap adapter to the case iron pipe. It has then been leaded into the cast iron hub.

As for 2 and 3, all I meant was using a long 90 vs to 45s to make the turn from the arm towards the double fixture connection.

I think it might be easier to find the 2 inch double fixture and just use reducers, but I can get to that piece when I take things out.
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
Thanks! So the 'lead pipe' I mentioned is like a steel pipe but it has been bent to conform to the turns they needed. Unlike the steel pipe, it is continuous and is one run from the trap adapter to the case iron pipe. It has then been leaded into the cast iron hub.
So maybe it is lead, that's beyond my experience.
As for 2 and 3, all I meant was using a long 90 vs to 45s to make the turn from the arm towards the double fixture connection.
Either a LT90 or two 45s is fine. It's common to use a 1-1/2" quarter bend, so that the bend doesn't stick out of the wall, but I think that's technically not allowed by the UPC. Two 45s would stick out even more than a LT90.

Cheers, Wayne
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
So maybe it is lead, that's beyond my experience.

Either a LT90 or two 45s is fine. It's common to use a 1-1/2" quarter bend, so that the bend doesn't stick out of the wall, but I think that's technically not allowed by the UPC. Two 45s would stick out even more than a LT90.

Cheers, Wayne
Thanks! Ans lastly, can this double tee be used? NIBCO® Hub ABS DWV Double Tee at Menards https://www.menards.com/main/plumbi...double-tee/i27045c/p-1444449190860-c-8562.htm
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
Thanks! Ans lastly, can this double tee be used? NIBCO® Hub ABS DWV Double Tee at Menards https://www.menards.com/main/plumbi...double-tee/i27045c/p-1444449190860-c-8562.htm
No, as I said you need a double fixture fitting rather than a double san-tee. E.g.


Although that's in PVC; I'm not finding it on menards.com in ABS, so you may have to look elsewhere if you need ABS. E.g.


Cheers, Wayne
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
No, as I said you need a double fixture fitting rather than a double san-tee. E.g.


Although that's in PVC; I'm not finding it on menards.com in ABS, so you may have to look elsewhere if you need ABS. E.g.


Cheers, Wayne
Thanks Wayne. SupplyHouse works great and I order from them. Thanks for all the help!
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
@wwhitney Hey Wayne, sorry to bug you but here is another think I was considering. The vent branch for the the current vanity sits around 38 inches which is roughly 6 inches above the floor rim (need to check again but if I recall correctly the current vanity sits at 30 inches). Our vanity is pretty low. We want to install the new one a bit higher but it will make the vent to be lower than the 6" minimum. Here is what we have.

pre-bath.png


Now I was wondering if it legal to add a wye that is angled at least 45 degrees with another 45 bend to raise the vent branch a bit. That can give me 4-5 inches of rise, but then again this vent branch is not going into the main stack so I am wondering if that is allowed. The rest I updated to match what you suggested
bath-proposed.png



This is the actual setup again
20230320_124903.jpg
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
No, all of your dry vents need to be pitched back towards the drain they serve at 1/4" per foot. [That's a UPC requirement; I think the IPC just requires they be pitched to a drain, not necessarily the drain served. MN uses the UPC.]

That's probably more important than whether they are 6" or 4" above the fixture flood rim. Obviously the correct solution is to raise all the horizontal vents and raise the connection point at the stack. Which it looks like you have access to.

Cheers, Wayne
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
No, all of your dry vents need to be pitched back towards the drain they serve at 1/4" per foot. [That's a UPC requirement; I think the IPC just requires they be pitched to a drain, not necessarily the drain served. MN uses the UPC.]

That's probably more important than whether they are 6" or 4" above the fixture flood rim. Obviously the correct solution is to raise all the horizontal vents and raise the connection point at the stack. Which it looks like you have access to.

Cheers, Wayne
Got it. So the 1st issue with my approach is that I am not pitching toward the sink drain and going back to the vent branch. 2nd issue is that even if I do that and pitch towards my drain, im creating a hump by elevating and then dropping. Right? Is that similar to an S vent issue? Just visualizing
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
Got it. So the 1st issue with my approach is that I am not pitching toward the sink drain and going back to the vent branch. 2nd issue is that even if I do that and pitch towards my drain, im creating a hump by elevating and then dropping. Right? Is that similar to an S vent issue? Just visualizing
The main issue with your latest drawing, UPC wise, is that left most red segment which is pitched towards the 2" black vent, rather than towards the lav drains.

There's no performance issue in regular use with the arrangement you propose. And the IPC would allow it, as it just requires each dry vent to be pitched to some drain, not the drain being vented. So it's nothing like an S vent, it's not going to cause your traps to siphon or anything.

Basically, I'm unsure why the UPC has that provision. Here's the reference, in case it helps:


Cheers, Wayne
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
The main issue with your latest drawing, UPC wise, is that left most red segment which is pitched towards the 2" black vent, rather than towards the lav drains.

There's no performance issue in regular use with the arrangement you propose. And the IPC would allow it, as it just requires each dry vent to be pitched to some drain, not the drain being vented. So it's nothing like an S vent, it's not going to cause your traps to siphon or anything.

Basically, I'm unsure why the UPC has that provision. Here's the reference, in case it helps:


Cheers, Wayne
So is the issue under UPC the wye that causes the elevation. What if I branch of with the wye but it pitches towards the double fixture?
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
So is the issue under UPC the wye that causes the elevation. What if I branch of with the wye but it pitches towards the double fixture?
Not 100% sure I'm following, but I don't see how that helps you. If the black horizontal (existing) vent is less than 6" above the flood rim level of the sink, there's no way to simultaneously comply with the 6" above flood rim rule and the pitches back towards the fixture rule.

Cheers, Wayne
 

John Gayewski

In the Trades
Messages
4,383
Reaction score
1,360
Points
113
Location
Iowa
No, all of your dry vents need to be pitched back towards the drain they serve at 1/4" per foot. [That's a UPC requirement; I think the IPC just requires they be pitched to a drain, not necessarily the drain served. MN uses the UPC.]

That's probably more important than whether they are 6" or 4" above the fixture flood rim. Obviously the correct solution is to raise all the horizontal vents and raise the connection point at the stack. Which it looks like you have access to.

Cheers, Wayne
I'm going from memory but I'm pretty sure vents can be level or pitched back toward the drain they serve.
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,854
Points
113
Location
Berkeley, CA
I'm going from memory but I'm pretty sure vents can be level or pitched back toward the drain they serve.
Yes, UPC does allow level (although IPC doesn't), thanks for the correction. Does help the OP with the existing horizontal vent that's too low if he raises the lavs, though.

Cheers, Wayne
 

KiviP

Member
Messages
36
Reaction score
4
Points
8
Location
St. Paul, MN
Not 100% sure I'm following, but I don't see how that helps you. If the black horizontal (existing) vent is less than 6" above the flood rim level of the sink, there's no way to simultaneously comply with the 6" above flood rim rule and the pitches back towards the fixture rule.

Cheers, Wayne
I am dumb. Did not get enough sleep. You are right because the main 2 inch vent branch will be below 6 inch and that whole branch needs to be 6 inch above the highest fixture it serves which is the lav...
 