ECM 3.0 motor ?

Users who are viewing this thread

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC
On these motors, Do they have delay times programmed into them or does the control board on the unit (gas pack)handle the delay times ? Mine is stopping as soon as the t-stat is satisfied, no delay to purge the heat out of the chamber.
 

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC

Fitter30

Well-Known Member
Messages
4,421
Reaction score
817
Points
113
Location
Peace valley missouri
Package unit fan is controlled by ignition control module. Both combustion fan and blower cycle the same time. Later units wait 120 seconds after burner shut off your unit didn't say. Heres the install manual page 16 diagram page 10 or 11 blower operation. Unit made by lennox surprised they have this manual on line.
https://pascalliedcdnep.azureedge.net/airease/AirEase_RPGE13_Install.pdf
 

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC
Package unit fan is controlled by ignition control module. Both combustion fan and blower cycle the same time. Later units wait 120 seconds after burner shut off your unit didn't say. Heres the install manual page 16 diagram page 10 or 11 blower operation. Unit made by lennox surprised they have this manual on line.
https://pascalliedcdnep.azureedge.net/airease/AirEase_RPGE13_Install.pdf

Thank you for the info ! I’ve looked high and low for an operational manual, I tested the control board for 24 vac going to the x13 fan (first one I’ve had experience with by the way ) I lost 24 vac as soon as t-stat satisfied. My original thinking was that maybe the module in the x13 held the delay, but now I know it’s the control board .

Thanks again !!!
 

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC
Thank you for the info ! I’ve looked high and low for an operational manual, I tested the control board for 24 vac going to the x13 fan (first one I’ve had experience with by the way ) I lost 24 vac as soon as t-stat satisfied. My original thinking was that maybe the module in the x13 held the delay, but now I know it’s the control board .

Thanks again !!!


Back to the drawing board lol
I installed new control board, same problem !
 

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC
Stat wires pull them off. R to w jumper wire let it fire remove w see what happens
M

Jumped across R-W , works just the same.
What I have notice is my wiring diagram on the unit doesn’t have a red wire coming from contactor to the Heat ACB terminal on control board like the wiring diagram shown in the install manual above.!
 

Attachments

  • 1C53123F-C14F-48D0-9C00-14F67A5146C8.jpeg
    1C53123F-C14F-48D0-9C00-14F67A5146C8.jpeg
    99.7 KB · Views: 111

Fitter30

Well-Known Member
Messages
4,421
Reaction score
817
Points
113
Location
Peace valley missouri
Never seen a thermostat like the one on the diagram. Any brand or numbers on that stat? Stat terminals 1-6-w-r-c Is there a jumper between R-W at the stat like the diagram? Motor termials 1 to 5- 4 heat, 2 cool, 1 fan only
 

WorthFlorida

6th clinical trail chemotherapy 5/15/24
Messages
5,788
Solutions
1
Reaction score
1,005
Points
113
Location
Orlando, Florida
Need to know the thermostat? is it a WiFi, a digital or a old mechanical. Thermostats will have a strap option or a program setting for the type of heat. Either fossil fuel (gas or Oil) or Electric heat. Many thermostats control the blower fan to give the results you're looking for. Thought the manual states its a non programmable setting within the furnace design as how long the fan motor starts and ends for each heat cycle.

Your very first question is No, ECM motor speeds are controlled with a low voltage, usually 0-10 volts on one signal lead. You stated that the 24 volts ac goes away when heat cycle ends and the fan motor stops.
 

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC
It’s a standard mercury bulb T-stat,

1EFEC47C-8AEA-4377-8089-0AF5229B4BF3.jpeg
5B78EE34-6019-40DB-B175-EFC366A24C6E.jpeg
 

Attachments

  • 1EFEC47C-8AEA-4377-8089-0AF5229B4BF3.jpg
    1EFEC47C-8AEA-4377-8089-0AF5229B4BF3.jpg
    45.9 KB · Views: 92

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC
Where's the 24 vac disappear? Like Worth wrote. Do have a pic of the motor name plate?
A
Where's the 24 vac disappear? Like Worth wrote. Do have a pic of the motor name plate?

I’ll have to recheck but I believe it was at transformer itself. Motor name plate as in indoor Blower motor ? I’ll try and get it for you.
Seems like it was a genteq motor also
 

WorthFlorida

6th clinical trail chemotherapy 5/15/24
Messages
5,788
Solutions
1
Reaction score
1,005
Points
113
Location
Orlando, Florida
That is a classic White-Rogers mechanical thermostat (4 wire) and it has no fan delay function. For heating 24v ac on the red lead (RH), when called for heat the mercury bulb closes the circuit and connects 24v ac to the white lead (W). The FAN "ON" position switches the 24v ac to the Green wire (G lead). This manually turns on the fan motor.

Cuzzinred; Has the fan delay to off of 120 seconds after the heat cycle ended ever work?
 

Cuzzinred

New Member
Messages
15
Reaction score
1
Points
1
Location
Richburg SC
That is a classic White-Rogers mechanical thermostat (4 wire) and it has no fan delay function. For heating 24v ac on the red lead (RH), when called for heat the mercury bulb closes the circuit and connects 24v ac to the white lead (W). The FAN "ON" position switches the 24v ac to the Green wire (G lead). This manually turns on the fan motor.

Cuzzinred; Has the fan delay to off of 120 seconds after the heat cycle ended ever work?
I can’t say if it ever worked properly, blower stopped working so I replaced it and noticed it wasn’t any delay. I’ve swapped blower with a know good one and replaced the control board, same results. I’m thinking about adding the missing R wire, do you see any problems with that ?
 

Fitter30

Well-Known Member
Messages
4,421
Reaction score
817
Points
113
Location
Peace valley missouri
Check to see if there is power coming off the control board to energize that added relay. If not can use a off delay relay w-c and wired the fan the same way.
 