I've completed all plumbing for my 2nd floor bathroom addition. I'm at a point where I need to tie into the existing 4" cast iron stack and have a couple different layouts I would like some input on.

Layout A
This uses one less wye and looks cleaner in my opinion. My only concern is that I have my full bath from upstairs merging with my 1st floor tub and then merging with my 1st floor lav. Looking at the dfu's for this I'm still OK for 3".

Layout B
I don't have the cleanout shown but this would be added on the bottom of the stack. This would require one extra wye connection and not look as clean. I would however separate the 1st floor lav from the others connected to the 3". Not sure if this really even matters.
 

Attachments

  • layout A.jpg
    layout A.jpg
    64.8 KB · Views: 147
  • layout B.jpg
    layout B.jpg
    22.9 KB · Views: 153

wwhitney

In the Trades
Messages
6,592
Reaction score
1,858
Points
113
Location
Berkeley, CA
The lav is 1 DFU, moving it to the stack is zero benefit, go with layout A.

Cheers, Wayne

P.S. If you have flexibility on how the lav drain approaches the stack, you can save one 45 degree bend by using two wyes with a bushing: 4x4x3 wye at the stack, the 3" side inlet get a 3" (possibly street) wye, whose side inlet gets your horizontal 3" drain, and whose straight inlet gets a bushing and the lav drain.

Cheers, Wayne
 