The picture shows the diverter valve for my roman tub. When feeding the tub spout, the pipes generate LOUD rushing water noise, heard throughout the house. When set to the hand spray, nice and quiet flow. Notice the multiple 90-degree bends in the line to spout. Could they be causing the noise? Is it obvious why the plumber didn't make a straighter run to the spout? Would a straighter run reduce the noise? Can the unused outlet on the diverter be used for spout? Can 3/4 inch copper tubing be used? This is all new construction and plumbing.
 

Attachments

  • Diverter.jpg
    Diverter.jpg
    28.2 KB · Views: 555

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
noise

1. ALL diverter valves specify that ANY unused openings should not be capped, but are supposed to be tied into one of the active device lines.
2. Probably because of the angles required, although 45 elbows would have been better.
3. The spout is not flow restricted so it can flow as much water as the valves can produce. That is what creates the noise. The shower is restricted to about 2 1/2 gpm and cannot create the flow necessary to make the noise.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks