lmei007 Member Messages 183 Reaction score 0 Points 16 Location Maryland May 24, 2011 #1 My 1st floor tub drain has a 1.5" vent. I am thinking move and add a vent for my basement counter sink horizontal drain. Can I connect the planned vent to that 1.5" vent? thanks,
My 1st floor tub drain has a 1.5" vent. I am thinking move and add a vent for my basement counter sink horizontal drain. Can I connect the planned vent to that 1.5" vent? thanks,
Terry The Plumbing Wizard Staff member Messages 29,942 Reaction score 3,483 Points 113 Location Bothell, Washington Website terrylove.com May 24, 2011 #2 You can connect the two vents together at 6" above the highest fixture flood level.
lmei007 Member Messages 183 Reaction score 0 Points 16 Location Maryland May 24, 2011 #3 greate! thanks
hj Master Plumber Messages 33,613 Reaction score 1,057 Points 113 Location Cave Creek, Arizona Website www.terrylove.com May 25, 2011 #4 quote; You can connect the two vents together at 6" above the highest fixture flood level. Technically, the requirement is 6" above the highest flood level OR 42" above the floor whichever is HIGHEST.
quote; You can connect the two vents together at 6" above the highest fixture flood level. Technically, the requirement is 6" above the highest flood level OR 42" above the floor whichever is HIGHEST.