Cool Buffalo New Member Messages 1 Reaction score 0 Points 0 Location tucson az Apr 11, 2011 #1 Can you ,per the international plumbing code come off above the middle of your horizontal waste @ a 45 degree angle(with a wye or combo) on a floor sink?
Can you ,per the international plumbing code come off above the middle of your horizontal waste @ a 45 degree angle(with a wye or combo) on a floor sink?
Tom Sawyer In the Trades Messages 3,625 Reaction score 35 Points 48 Location Maine Apr 12, 2011 #2 not unless that 45 has been rolled up so that it rises vertical. You can not flat vent