View Full Version : Shallow Well Lawn Irragation pump cycle problem
lfmgtc59
03-12-2011, 06:41 AM
I inherited a shallow well lawn sprinkler system that was disfunctional. After a lot of effort it is now up and running... almost.
Setup:
9 well points on 1-1/4" pipe (5 of the wellpoints are 1-1/4", the remaining 4 are 1")
The wellpoints are 13' deep with approx 5 - 6 feet of water.
There are check valves at the top of each well point
Well points are approximatly 10' apart
The pump is a Sta-Rite DS2HE-103 (all seals have been replaced)
Main inlet line is 1-1/4"
Main outlet, and the lines to the valves are 1"
On the outlet side I have a fitting (a) to allow me to add water / pressure to the system and just downline from that a valve to be able to isolate / shutoff the main line to the valves. There is also a pressure cut off switch just on the outlet side of the pump.
There are 9 valves.
If I pressurize the system by connecting a hose from the city water to the outlet side (a) the entire system with valves off will hold 40psi pretty much indefinitly even after the city water is cut off, so it appears there are no bad check valves and no leaks out to the valves.
There are two issues:
1. It takes about 20minutes for the pump to begin to make enough pressure to actually run the sprinklers - Is this normal?
2. Once the cycle has run and the valves shut the outlet pressure reaches 40psi the pump shuts off, but immediatly the pressure drops past the cut in pressure of around 20psi and the pump begins to go through a very short cycle... this continues until I kill the power to the pump, then pressure immediatly drops to 0.
Can anyone help me out on this, I have some ideas, but don't want to cut the system up trying them when I'm not sure whether or not they will work.
Any assistance is much appreciated.
Thank You!!
Lee
lfmgtc59@aol.com
LLigetfa
03-12-2011, 06:56 AM
I think I need a check valve on the outlet side and to place the pressure switch immediatly downline of that, so that the pressure in the outlet side is maintained until a valve opens, pressure drops and the pump kicks in... Is this right??No. You stated the pressure switch hangs off the side of the pump. A checkvalve on the outlet would isolate the outlet pressure and the pump would come back on.
If you want to prevent pressure from backflowing to the inlet, you need to put the checkvalve on the inlet of the pump, not the outlet. I doubt that will solve your problem though. No pump should take 20 minutes to make enough pressure to use unless you have an extremely large air charged storage tank.
I wonder... with multiple intake sand points, what would prevent the pump from drawing one down more than the other and suck air?
lfmgtc59
03-12-2011, 07:10 AM
Thanks for the reply
... let me clarify
The pump manual specifically says not to use a pressure tank as this presents serious risk of explosion, so there is not one.
At present the flow is: Well point ->checkvalve (at each well point) -> 1-1/4" pipe -> pump -> 1" reduction -> Pressure switch & gauge -> valve with hose attachment -> manual shutoff valve -> main 1" feed pipe to valves
What I proposed was Well point ->checkvalve (at each well point) -> 1-1/4" pipe -> pump -> 1" reduction -> gauge -> valve with hose attachment -> checkvalve -> Pressure switch -> manual shutoff valve -> main 1" feed pipe to valves
I used the manual shutoff valve when I was troubleshooting leaks in the system to isolate the inlet and outlet sides.
I suppose it is possible for the system to pull some air with the multiple well points, but the pressure is pretty steady through 70 minutes of operation. If I run the system an additional 20 minutes you can begin to see fluctuations in the pressure and hear some air flowing through the valves.
However the real issue is after the valves shut and the pressure cut off of 40 is reached. That is when the cycling starts and as I say goes on until I cut the power.
LLigetfa
03-12-2011, 07:30 AM
If the pressure switch shuts the pump off at 40 PSI, where is this serious risk of a rupture? With the pressure switch set so low, and if the pump capacity exceeds the consumption, in the absense of a pressure tank, short cycling is inevitable. No checkvalve on the outlet will solve that.
What is the max pressure that the system can safely handle? As you increase the pressure, the pump will produce fewer GPM so the pump will be less likely to exceed consumption.
Maybe valveman will come along and suggest a tank or CSV/tank combination to reduce the cycling.
lfmgtc59
03-12-2011, 08:16 AM
I agree with what your accessment on the pressure tank, I don't see how the pump could possibly develop enough pressure to explode, but not being a diy'er on this I figured I would follow the directions.
I have been out doing some more checking...
It appears that even with the check valves at the well points, the 1-1/4" feeder pipe the well points are attached to is this morning near dry. The pump maintains prime (there is water in it), but the lines feeding it are basically dry... I thought the check valves were supposed to stop that.
This is why the 20 minute wait for pressure, only today I had to "fill" the feed lines back to the well point check valves in order to get the pump to draw.
The system still maintains 40psi when pressurized, so it does not appear I have developed any leaks...
So where does the water go and how do I fix it??
Signed Perplexed
lfmgtc59
03-12-2011, 08:40 AM
Additionally...
If I fill the feed lines using the house water I can build up 40psi in the entire system. If I then close the manual valve to the main outlet line that feeds the sprinkler valves, and bleed of pressure and water via another valve on the outlet side, as the pump is running and making pressure on the outlet side, I can hear bubbles coming up through the feed lines from the well points...
If I shut the valve I am using to bleed pressure of with the bubbles continue and the pump continues cycling if I shut off the main feeder line the pump and pressure stablize and shut off.
It is almost as though when the suction in the feed line reaches the point of opening the check valve the air at the top of the well point enters the system and the water in the system is running back into the well point... that is the only place I can figure air would be entering the system...
Any experts out there willing to give me the benefit of your experience?
valveman
03-12-2011, 08:41 AM
Without a pressure tank, you have nothing to maintain pressure after the pump shuts off. Just the check valves closing means a little water has to go backwards to do that, and you don’t have a tank to supply that water, so the pump comes right back on. The tank would also supply water back towards the check valves. So if there is a leak between the check valves and pump, you wouldn’t lose prime. Your pump will have to come back on when the tank is empty. The tank maybe able to supply a small leak for days or weeks before the pump must start.
I can’t imagine a pump that comes with a pressure switch attached NOT having a pressure tank. That is just crazy advice. Get a pressure tank!
You also probably have a leak on the suction side. But the pressure dropping as a tank drains to the leak will help you find the leak.
lfmgtc59
03-12-2011, 08:51 AM
valveman...
I appreciate the advice and the explaination - Like I said I inherited the system which was not working at the time... so I'm not sure if the pump came with a pressure switch or not. The hand scrawled instructions I found in the valve control box had the first and last step of running the system as turning on and shutting off the breaker, so my guess is that it never worked right to begin with...
Anyway - Where would you add the pressure tank into the system?
Current arrangement: Well point ->checkvalve (at each well point) -> 1-1/4" pipe -> pump -> 1" reduction -> Pressure switch & gauge -> valve with hose attachment -> manual shutoff valve -> main 1" feed pipe to valves
How would I determine the size of the pressure tank?
Thank You
Lee
LLigetfa
03-12-2011, 09:10 AM
To quote valveman, there are two kinds of checkvalves, those that leak and those that will eventually leak. A checkvalve needs pressure to maintain the seal. You cannot expect a checkvalve to hold in the absense of pressure.
Even if the checkvalves don't hold at the sand points and the water falls back, that doesn't explain the air in the collector pipes. The air has to be coming from somewhere. I'm not saying you don't need the checkvalves, because you do. They act as ratchet stops so that as the pump goes through spurts of suction/no suction, the gains it makes don't fall back.
As for a tank, I would put it as close to the pump discharge as possible and I would mount it higher than the pump. I would not use a bladder tank, just a free air tank without air volume control. The tank will act to bleed the air during start/prime, and the water in the tank will aid the self priming during start.
I don't know how much pressure the pump can produce nor how much it can safely tolerate. I couldn't find a manual on your exact model but the manual for a similar model makes no mention of how much pressure it can produce or tolerate. None the less, an air over water tank will help reduce pump cycling but what you really need to do is tune the demand to the supply, meaning don't close off more than the pump produces at 40 PSI.
lfmgtc59
03-12-2011, 09:45 AM
Based on my tests the peak pressure this pump generates is about 45-48 psi when it first kicks on. The highest pressure it seems able to maintain over any period of time is right around 40 +/- 2.
A couple of questions:
I am familiar with the operation of a bladder tank as I had a house that utilized one when I was on a spring fed water system, however, I am not familiar with a free air tank.
What size tank am I looking for?
Should the tank be empty when hooked up (full of air) or water?
Will I need a way of draining the tank as I required with my bladder tank?
... Guess that was three questions.
Thank You
Lee
LLigetfa
03-12-2011, 10:10 AM
Since the tank really is just to absorb fluctuation in pressure it would act more like a giant water hammer stop, so size is not all that important. I'd go with one that has around 5 gallons total volume. It would be full of air to start and the air would compress allowing water into the tank as the pressure builds. If it were to ever waterlog which I doubt, you would need some way to drain it or some way to pump air into it. More than likely, it would accumulate enough air on its own and surplus air would just go out with the water.
valveman
03-12-2011, 12:44 PM
I would use a bladder tank. A 20 gallon size tank will hold 5-6 gallons of water. This size tank is large enough if you match the zone size to the volume of the pump. With that type of pump you can actually increase the pressure switch setting until the pump continues to run as long as there is a couple of GPM being used. Which kind of makes it work like a CSV.
You shouldn’t need a bladderless tank to deal with the air. If the pump still gets air after the tank is installed, you need to find and fix the leaks in the suction. Otherwise you could draw in air and lose prime while the pump is running. Which would burn up your pump. Losing prime while the pump is running is much more possible after installing the pressure tank. When it gets down to a couple of GPM before the tank fills, it is much easier to draw in air than water, and the pump loses prime. It doesn’t do that now because you are always pumping max flow. At max flow the small air leak just mixes with the water and you never notice it. At minimum flow the air will come in easier than water, and you will lose prime before the pressure gets to the shut off point.
After adding a tank, there should be no spurts of suction/no suction or you still have a problem.
lfmgtc59
03-12-2011, 01:24 PM
Hey LLigetfa / Valveman:
You called it absolutly correct!! :-)
Ok, I added the tank... I had a neighbor with what looks to be an old 2 or 3 gallon tank that I hooked up. It actually works pretty decently. The system seems to start at 20psi and shut off at 40psi correctly with just a couple of cycles. It runs at between 24 and 36psi with the sprinkler system in operation with initial drops down as a new valve system opens up. There seems to be a lot of crud coming through, so the heads are clogging, but I guess that is just the result of it sitting for almost 5 years.
It holds around 26psi when it shuts off.
Based on what I am seeing I think the bigger tank you suggested would be a good investment. The local Lowes smallest tank is 7 gallon with a bladder. Do you think that would work Ok as long as I set the initial pressure in the tank at around 23?
Thanks again... it feels really good after what I have been through getting this up and running to see it actually work correctly.
Lee
LLigetfa
03-12-2011, 01:56 PM
Looks like valveman and I disagree on the style of tank. Sure, a bladder tank will work to reduce cycling but if properly precharged, a bladder tank holds no water at 1 PSI. On impeller pumps, I like to have a reserve of water above the outlet. When starting the pump from zero, this "head" of water helps to purge the air yet drops back to the pump to aid the self priming.
Back in my youth, I worked with a lot of gas and diesel powered impeller pumps on pipeline construction and learned how to get them going faster than most anyone else. It looks like in your case, your could use the city water to put a head of water in the tank so perhaps it matters less. Bladder tanks are easier to find at big box stores.
As for crud clogging the sprinkler heads, don't most setups have large Banjo filter screens?
12847
valveman
03-12-2011, 04:05 PM
OK! I see exactly what you mean. We use to keep gallon jugs of water sitting in the well house to prime with. We even had a bladderless tank. There was just a check valve between the pump and tank or we could have used that for priming as you said. Removing that check valve would have probably saved me filling about a thousand jugs of water. :(
But like you said, he has a garden hose from another water source. So I still think the bladder is best for this one, and as long as the pump doesn't cycle running the smallest zone, a 7 gallon bladder tank more than sufficient.
lfmgtc59
03-12-2011, 04:35 PM
Hey Guys
Ok here is the outcome...
I couldn't find a bladderless tank, so I went with the bladder tank. Because of size and mounting restrictions in my application I went with the 7 gallon tank as the next largest was 20 gallon and to large to fit.
I pre-charged the tank at 18psi. I fully primed the system back to the wellpoints using a couple of valves at the end of the lines I put in for that purpose. At the same time I pre-charged the output side to the spinkler valves.
It took just 2 minutes to get up to pressure once I turned the pump on and started the system and the valves started opening.
The system held a nice even pressure through the 9 zones around 30psi. When the last zone finished the pressure gradually climbed to 40, the pump shut off and there was a sudden pressure drop, but only to 36psi where it stopped rock solid.
I have turned the breakers off for the night (did not want to take a chance with the pump). I will see tomorrow if the pressure has held overnight. It has held 40psi overnight before, so I can't see there would be a problem. If so I will flip the breakers and start the system manually in the morning.
I guess that will be the real test to see if it all fires up tomorrow.
I REALLY APPRECIATE ALL THE HELP!!!
I'm pretty sharp on researching most of this stuff, but what is in the books isn't always exactly what you find in the field - as you guys probably know - so it really helps to have someone who has been there done that letting you know where you've gone wrong.
Thanks Again... I'll let you know how it comes out tomorow.
Lee
Lee
lfmgtc59
03-13-2011, 06:09 PM
Ok this morning the pressure was at 0 psi. Because I had switched the breaker off, I don't know if the pump would have kicked on at 20 psi and been able to re-pressurize the system or not.
As there are no leaks in the pipes, joints etc. the only thing I can think of is leaks through the check valves back into the well points.
I had to re-prime the system, and even at that it took 15 - 20 minutes to build enough pressure to properly work the sprinkler system. You could hear at the sprinkler valve that there was a lot of air being pushed through the line. My thought is that there are 9 well points and the water is 8' below surface, so there is a lot of air to move before the pump really can get up to normal operating pressure / volume.
Is that a valid assumption?
After that, all seemed to go well (no pun intended). I ran it through an abbreviated sprinkler schedule and when the cycle ended the pump built up to 40 psi and cut off as it was supposed to. Pressure stabilized at 36 psi again.
Leak down by the hour has been as follows:
1 - 36 psi
2 - 36 psi
3 - 35 psi
4 - 35 psi
5 - 35 psi
6 - 35 psi
7 - 35 psi
8 - 35 psi
9 - 35 psi
10 -
11 -
12 –
Based on the 0 psi this morning, this is rather unexpected. The pump has not kicked on at all, so the pressure has been steady. I'm going to monitor for another few hours and see what happens.
So what should I see happen if the system is functioning the way it should?
Thank You
Lee
LLigetfa
03-13-2011, 06:26 PM
There must be more than one leak. If it were just leaking back to the wells, the pipe would not fill with air. Somewhere air has to be leaking into the system.
lfmgtc59
03-13-2011, 07:28 PM
clarification:
"leak down by the hour" may be misleading - these were the actual pressure readings by the hour... actual leak down was only 2 psi over a 10 hour period
I have all the horizontal pipes and the first foot or so below the check valves on the well points fully exposed and I cannot find any evidence of a leak even when pressurized to 40 psi over a several hour period.
Not trying to be argumentative, just trying to fully understand... But since the water in the well points is 8' below ground level, wouldn't that mean that there is an 8' column of air in the well point vertical pipes when the system is at rest?
Also, I cannot understand why over 12 hours yesterday I lost 36 psi and so far over 10 hours today I only lost 2 psi...
Thank You
lfmgtc59
03-14-2011, 05:40 AM
Its now been 21 hours and I have lost 4 psi... course the temperature at the start was 75 and now is 56... which could account for some pressure loss as the pipes, pump, and tank are exposed. Its supposed to climb to 80 today, so I will find out.
What should I expect to happen here? Should the system hold pressure indefinitly - in theory I would think so, but in reality what would you say should happen?
Thank You
Lee
valveman
03-14-2011, 08:30 AM
Even though it is 8’ from the check valve down to the water level, it should stay full of water. The check valves act like putting your finger on top of a straw full of water. The water can’t get out until you remove your finger and let air in. 9 checks valves leave 9 places to fail. With the power off, if any of these checks leak back, you are going to lose prime. With the power on, the pump should come on and refill the pressure tank, after the water in the tank leaks back through the bad check. So if you leave the power on, the pump will cycle on and off while no water is being used.
Worn check valves always close differently. One time it may seal pretty good. The next time it may not seat in the same place and won’t seal at all. One or all of your check valves is leaking back. The process of elimination maybe the only way to find it.
lfmgtc59
03-14-2011, 08:39 AM
Thank you Valveman... that makes a lot of sense.
Its a real bummer about the check valves though... I just installed new ones.
I did notice when flushing the lines that I'm getting some crud... less now I've done it a few times. So it is quite possible something gets stuck in the seal causing it to fail to seal.
So far this is what the pressure over the last 24 hrs looks like - the pump has not kicked on:
1 - 36 psi
2 - 36 psi
3 - 35 psi
4 - 35 psi
5 - 35 psi
6 - 35 psi
7 - 35 psi
8 - 35 psi
9 - 35 psi
10 - 34 psi
11 - 34 psi
12 - 34 psi
13 - 34 psi
14 - 34 psi
15
16
17
18 - 34 psi
19 - 33 psi (6:30)
20
21 - 32 psi (8:30)
22
23
24 - 34 psi (11:30)
I think the move down from 34 - 32 and back up was caused by cooling and heating (about 20 degree difference in ambient temp, plus sun exposure) as the pipes are exposed at this time.
I appreciate all the assistance!
Thank You
Lee
valveman
03-14-2011, 02:00 PM
That many check valves and pumping crud, I would get a low pressure cut-off switch (FSG2M4). PITA to prime with but, will save your pump if you lose prime.
lfmgtc59
03-14-2011, 02:53 PM
Valveman:
Would this do the job?
20/40 Psi Pressure Switch
Brand: Square D
Model: FSG2J20M4
SKU: 303904
20/40 PSI Standard Pressure Switch With Low Pressure Cutoff, 1/4" - 18 NPSF Internal Thread Opening, Low Pressure Setting At 20 PSI, For Electrically Driven Water Pumps.
An integrated unit would be easier to plumb in at this point.
Thank You
Lee
P.S. Pressure still holding at 34
valveman
03-14-2011, 04:43 PM
Yep, that is the one I am talking about.
lfmgtc59
03-14-2011, 05:49 PM
Lowes and Ace do not carry them, so I ordered it from drillspot.com. It will be about a week or so, so until then I'll cut the breaker and deal with it, as I cannot risk burning out the pump..
At what psi does the low pressure cut out activate?
Thanks Again
Lee
LLigetfa
03-14-2011, 06:05 PM
Approx 10 PSI
lfmgtc59
03-22-2011, 03:40 AM
Good Morning valveman / LLigetfa
OK... the system has been working more or less - had to fix another couple of cracked pipes on the sprinkler head side of the valves and my pressure switch has some issues (it does not want to kick on until somewhere between 5 & 15 depending on the day and sometimes does not want to shut off at 40), but that will be fixed as soon as he replacement arrives today. However, there is another rather puzzling issue:
The sprinkler system runs through its cycle, the last zone up runs about 30 psi. It closes and the pump builds up to around 39, then begins to lose pressure in spurts. It starts going through this sort of 5+/-lb pressure "surge" (you can hear what sounds like water like shooting into the tank at each surge) but after each surge it drops to a lower pressure. This levels off around 20 / 25 and if I don't intervene just stays there running. It has happened twice.
The first time I cut the breaker, shut the valves to the well point side of the pump and the sprinkler valve side of the system, thus isolating the pump and tank. Since I was going to put on a better gauge I decided to do it then. To my surprise only compressed air came out when I removed the valve. very little water.
The second time it happened, I switched one of the zones back on... within a couple of minutes it was running 30 psi and running the system just fine, when the zone shut off, the system gradually built pressure to 40 and switched off as normal.
Ok... its done it again. I followed the same approach as above in the second time with the same result.
I at first thought I had bled the well dry, but as in the second time around I was pumping 30psi out to the spinklers when I opened the zone valve... I suspect that is not the case...
Any ideas?
Thank You
Lee
valveman
03-22-2011, 09:01 AM
You have a leak in one of the suction lines. When you are pumping full flow to the sprinklers the air leak doesn’t amount to much. But when the sprinklers are off and you are filling the pressure tank, the flow rate gets so low that it is easier to draw in air from the leak than water from below. You can find a leak with shaving cream. It will make a hole in the shaving cream where it sucks in air. Or you can rap the connections with plastic rap. When you rap the connection with the leak, the surging will go away.
lfmgtc59
03-22-2011, 05:58 PM
Much appreciated valveman... it must be a very slow leak indeed...
Fortunatly the way the system is set up once the problem occurs I can shut off the two main lines leading to the well points individually. That way I can tell right away if it is a leak above or below grade and if below which way...
Hopefully it is above grade as I just filled all that in and seeded last weekend... Anyway the info on the shaving creme and plastic rap is appreciated.
I suppose where ever the leak is will mean cutting it all apart again... as it is in suction any chance in putting something on the leak and it getting sucked in and sealing??
Again, Thanks for the advice.
Lee
valveman
03-23-2011, 06:16 AM
If the leak is in a threaded joint then no. If the leak is in a glue fitting, then let it suck in some more glue. Sometimes it works.
lfmgtc59
03-30-2011, 08:41 AM
I did find a small leak (very small) at the PVC to Iron threaded joint at the pump. The thread on the pump is not the best, but it is all I have, so I laid the heavy duty pink Teflon tape to the joint and have had no leaks since…
However… (does this ever end??)
Now it may run through the 9 zones 4 or 5 times over a two day period without a hitch, but for no apparent reason pull a bunch of air on the 5th or 6th time through and get hung around 15 – 25 psi and thus not shut off.
The following all occur regularly:
1. Runs through all 9 zones with no perceivable issues at all.
2. Sometimes, perhaps midway through a full nine zone cycle (it differs from run to run) all of a sudden a mass of air hits the pump (I am able to tell by the sound, but also visually at the clear filter I installed). In mid cycle the system seems to handle this with no apparent problem.
3. Sometimes, at the end of a full nine zone cycle all of a sudden a mass of air hits the pump (I am able to tell by the sound, but also visually at the clear filter I installed). Because the flow has been shut off as the cycle is over, this appears to cause some type of cavitation, which seems to allow the pump to not drop below 10 psi (low pressure cut off), while not allowing the pressure to build above 25 psi.
Thus the system just runs and runs, builds up heat, eventually creates steam (did this once), but at any rate just keeps running and running.
If I open any of the sprinkler valves and give the system a flow, in about 2 – 3 minutes it is making pressure and working fine. Then nine times out of ten once the valve shuts the system builds to 40 psi and shuts off, and hold about 35psi.
My guess is something is leaking in one of the well points below the check valve???
Also getting very fine sand in the filter…
Any ideas?
Thank You
Lee
valveman
03-30-2011, 10:04 AM
Any ideas?
Thank You
Lee
I think you are right, and that could also cause the sand.
lfmgtc59
03-30-2011, 10:37 AM
This does not sound good...
With nine well points, is there any tricks of the trade that might help isolate which one is the problem?
Thank You
Lee