View Full Version : New House old well
dubay
10-21-2005, 07:13 PM
House is in northern maine, on an Artisian well, Am using a jet style goulds pump, pump is loosing it prime, and when the pump is running, I get only about 27 PSI, pump was in the basement of old house. basement was filled in and concrete slab poured for new house, lines were spliced and buried. I think I already know the answer to this question but am just making sure im right. either im leaking air somewhere in the line or the jet is clogged.
B Dubay
Pumpman
10-21-2005, 10:01 PM
Or, the footvalve is bad. I'm assuming, since you said this was an artesian well, that it is under pressure, so it shouldn't be a water level problem.
Ron
rshackleford
10-22-2005, 05:29 PM
Artesian well or flowing well?
Could the new elevation of the pump mean that it is no longer getting pressure from the aquifer or is this a flowing well that water has shutin pressure at surface? Perhaps if this is an artesian and the static level was below natual grade there was never a footvalve installed becuase it always had formation pressure.
speedbump
10-23-2005, 08:40 AM
With only 27 psi, I would say the jet is plugged. If you had to do some plumbing with the system you may have knocked enough scale loose to plug it.
Flowing well or not, a plugged jet is going to cut your pressure about in half.
The footvalve would be necessary to hold the system pressure once the pump shuts off.
bob...
rshackleford
10-23-2005, 08:49 AM
Good point on the check valve. thanks.