Validate drain and vent plan
PJR
I'm redoing our master bath and as part of the remodel we are swapping the location of the shower and the tub and making the shower bigger. The shower has a 2" drain and a 1 1/2 vent coming off the drain line and up the wall to the roof. The tub has a 1 1/2 drain that dumps into a 1 1/2 pipe in the wall that is also vented through a 1 1/2 vent to the roof.
Can I dump both the shower and the tub to the 2" drain and then connect the vents as shown in the attachment? I believe I need to give the shower its own vent line since it is outside the 5ft distance for the 2" wall vent. Points I would like to have verified
1) Can i run both the shower and tub to the same 2" drain (sloped 1/4" per foot)
2) Is it necessary to use a 2" ptrap and drain line on the tub since it is more than 3 ft from the vent
3) Should I use a Wye fitting to connect the tub drain line to the drain from the shower? Is there a better recommendation?
4) When running the vent for the shower off the 2" drain line what do I need to think about? Does the vent need to stay vertical until it is 6" higher than the shower drain or the tub overflow?
What else am I forgetting?
Thanks for your advice
Below approx. 42" above the floor, the vent can not be horizontal ( defined as less than 45º slope)
Thanks for the reply even though it kind of shoot my plan down :) Can you suggest any alternatives? The 2" drain line is in the 2 joist bay so I can't go vertical more that 20" (tub deck height).
I believe you are allowed to wet vent in Illinois, so the drainage "looks" ok, but your venting does not. It is difficult to really approve of your drawing as the actual installation could be interpreted in many ways.
If I put a pony wall between the shower and the tub I could meet the 42" vertical requirement on the shower vent. Would that make the rest of the design valid?
thanks again