My house was built in 1930 - I'm not sure how old the boiler system is, but based on my research trying to get some questions answered, I think it must be quite old since I don't have all the bells and whistles in the equipment on my system.
I have a New Yorker Boiler, model FR. It looks like an FR-122 except for that there are no digital controls, so maybe the earlier model of that? Coming from the top of the boiler is a single pipe which then tees to provide hot water to two loops.
The first loop provides heat to my 8 radiators in the house. The second loop provides heat to 4 floor radiators in a room that was added on around 30 years ago. Each loop has its own thermostat-controlled valve. For the return piping, both loops come back together, then travel through an old Grundfos circ pump and back to the boiler.
Here are my current symptoms:
1 - If the main part of the house is cold enough so that its thermostat relay is energized, I can trace hot water from the boiler to the first loop, to the attic, down the wall, through all 4 radiators upstairs and to the 4 radiators downstairs. However, the heat in 2 of the downstairs radiators stop about halfway down the radiator and the outlet pipe is not hot. The other 2 downstairs radiators are hot all the way to the floor. However, the return piping to the boiler is not hot either (both in the crawl space and directly next to the boiler). Additionally, the add-on room floor radiators do not have any heat whatsoever.
2 - If the main part of the house is warm enough so that its thermostat relay is not energized, the add-on room starts to warm up. The return water into the boiler is at least warm. It is uncommon for me to be in this scenario for too long since the main part of the house cools off so I find myself back in the first situation.
I have been troubleshooting my system for weeks, so I have much more information to offer if it will be valuable, but I can sure use some help heading down the right track. I can even draw a sketch of my system or post pictures if necessary.
Thank you,
Brian
I have a New Yorker Boiler, model FR. It looks like an FR-122 except for that there are no digital controls, so maybe the earlier model of that? Coming from the top of the boiler is a single pipe which then tees to provide hot water to two loops.
The first loop provides heat to my 8 radiators in the house. The second loop provides heat to 4 floor radiators in a room that was added on around 30 years ago. Each loop has its own thermostat-controlled valve. For the return piping, both loops come back together, then travel through an old Grundfos circ pump and back to the boiler.
Here are my current symptoms:
1 - If the main part of the house is cold enough so that its thermostat relay is energized, I can trace hot water from the boiler to the first loop, to the attic, down the wall, through all 4 radiators upstairs and to the 4 radiators downstairs. However, the heat in 2 of the downstairs radiators stop about halfway down the radiator and the outlet pipe is not hot. The other 2 downstairs radiators are hot all the way to the floor. However, the return piping to the boiler is not hot either (both in the crawl space and directly next to the boiler). Additionally, the add-on room floor radiators do not have any heat whatsoever.
2 - If the main part of the house is warm enough so that its thermostat relay is not energized, the add-on room starts to warm up. The return water into the boiler is at least warm. It is uncommon for me to be in this scenario for too long since the main part of the house cools off so I find myself back in the first situation.
I have been troubleshooting my system for weeks, so I have much more information to offer if it will be valuable, but I can sure use some help heading down the right track. I can even draw a sketch of my system or post pictures if necessary.
Thank you,
Brian