WC venting, UPC code

DavidTu

Member
Messages
261
Reaction score
1
Points
18
Location
Seattle, WA
I have the following situation for a WC (see pics)... the WC is dropping to a closet bend then going down for around 1ft at 45-deg... I can vent it either on the 45-deg drop (so about 10" below WC) or after it levels out (around 14" drop from the WC). I cannot vent before dropping down b/c there is a chimney in the way and I must turn and drop right away.

Normally, for a fixture the vent take-off must be above the p-trap weir; in a WC of course that is not possible... but I am wondering what the acceptable limits are... or how far can I drop below WC closet flange before venting?

So am I ok with alternative #1 or #2 (see pics) or must I do something else?

Thanks!
 

Attachments

  • Ravenna Powder WC 2.jpg
    Ravenna Powder WC 2.jpg
    43.8 KB · Views: 1,384
  • Ravenna Powder WC 3.jpg
    Ravenna Powder WC 3.jpg
    46.7 KB · Views: 1,582
  • Ravenna Powder WC 1.jpg
    Ravenna Powder WC 1.jpg
    36.1 KB · Views: 1,396
For the water closet, either would be fine. It needs to be a wye or combo fitting on the vent.
For a water closet, you could even have taken it off the vertical with a wye. In King county, the vent should be within six feet of the flange.
 