OK, inspecting a new building for ADA compliance and found this in on two of the washbasins. Now they cut into the protective wrap and it is forward facing hitting a chair user right below the knees... but it also just seems a weird thing... it's a tiny url link...


http://tinyurl.com/2u8du69
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
That would be for priming the floor drain below.
Without that, the p-trap water could evaporate.

If you ever go into a public bathroom, and it smells badly, take a paper cup and fill the floor drains with water.

Here is a picture of a p-trap with the inlet for the priming.

attachment.php
 

HoracioO

New Member
Messages
26
Reaction score
0
Points
0
Location
NV
Ahh Thanks Terry! It seems so much of an afterthought, oddly enough only one restroom had it in there despite this building having around 16+ restrooms.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
It is a trap primer, although they are usually attached at the rear, not the front. and you only need one for each floor drain. Other drains may have different means of maintaining the trap's seal.
 