Lakee911
09-21-2005, 01:13 PM
Hi all,
Curious to see what you guys recomend for using DWV for drain for a condensate pump. Is this the correct procedure? Condensate Pump Drain to air gap to P trap to DWV system? Any better ideas? Air gap needed? If Condensate drain (from A/C) has a trap, do I still need the airgap and trap after the pump?

Thx
Jason

hj
09-21-2005, 02:54 PM
The pump makes the condensate connection from the AC an indirect connection so it does not need a trap. The pump should have a check valve on its discharge connection, so you can make any type of connection to the DWV that will work.

Lakee911
09-21-2005, 05:52 PM
Oh ya, it does. Thanks

Jason