1. You cannot use a double "Y", (or a double sanitary tee, or a sanitary cross), where they come together.
What is the proper connection? The intersection is only about 2 feet from the bathroom fixture and ~43 feet from the other fixture. There is enough drop that I could probably use two sanitary tees, one almost right on top of the other.
2. You should NOT use 1 1/2" below that point either.
2" is okay, I presume? Does this then require larger vent piping?
3. If the two sinks are actually 45' apart you should not be using 1 1/2" pipe for the drain lines.
So, the 43' section would need to be 2"? Can the drain from the sink close to the intersection be just 1.5"? Out of curiosity, how does the length affect needed flow?
4. I do not consider a SaniFlow installation to be one of the better ideas as a long term solution.
Don't know what I can say. I think from a budget and desire perspective, the project is out of the question if it involves digging up the slab.