The circulators should have been on the feeds
my old circulators were on the return and the install instructions said they could be on the return. Will they be ok?
The relief valves need to be piped to within 6" of the floor
that's on the list
Is that a plug in the vent opening of the back flow preventer?
yes it had a slight drip. Any idea why the drip?
The oil line needs to be clipped up and protected
how should I protect it? With 2*4s boxed out or somthing?
The circulator on the indirect should not be down there on the floor.
your right I'll plum it next to the others
The wiring needs to be straightened out and attached better
done
The water feed valve shoud be piped above the expansion tank.
could that be the reason the back flow preventer had a slight drip to it.
Where is the low water cut off?
The instructions said it was optional and I was going to buy it anyway but the supply house said I didn't really need it. I guess you recommend one