I only think they're goofy because I was not trained on the IPC or the other codes just like I'm sure some of the code requirements by the UPC sound very strict to people in the IPC. The IPC is alot more forgiving when it comes to wet vents and vertical offsets in trap arms which I've never seen, let alone been allowed to do. The UPC doesn't allow 2 traps on 1 trap arm. The picture that shows the shower, shower trap arm and vent upstream of the toilet, toilet trap arm and wet vent would not be allowed. The shower would have to tie in downstream of the toilet trap arm after the vent. The UPC also considers a wet vent to be a vent and therefore needs to tie in above centerline of the toilet trap arm. As for santees, below the flood level rim they are considered the same as 1/4 bends and need to be installed the same as any drainage fitting, so they'd never be allowed on their backs or horizontal to horizontal. The only reason the IPC and UPC haven't merged is simply the cost to people who have to learn a new code.