Does anyone know a good link that talks about testing drain lines? I searched and searched.....I just replaced all the cast iron with 4inch PVC, and I want to test all the connections. Any hints? I read use a 10ft column of water which creates ~ 10psi. In order to fill it up, I would need to fill up 16 feet up. Is that the best way?

Thanks,

Dan
 
Does anyone know a good link that talks about testing drain lines? I searched and searched.....I just replaced all the cast iron with 4inch PVC, and I want to test all the connections. Any hints? I read use a 10ft column of water which creates ~ 10psi. In order to fill it up, I would need to fill up 16 feet up. Is that the best way?

Thanks,

Dan

That would be OK. In some towns we had to flood the system through the roof.
That put a 30' head on the pipe.

John
 
I think it depends on what code you use in NY. I would fill the all of the waste piping with water until it came out of the vents on the roof. The 10ft head of water results in around 5 lbs of pressure. The idea is to have at least a 10ft head of water over the HIGHEST joint in the system which would mean your last vent joint. Sometimes that's not possible so just filling the system with water through the roof should be adequate.
 