I am look for some guidance with a half bath plumbing layout. This will be all new plumbing and tying in to the 4 inch sewer line in the basement. Also this is on the first floor and no plumbing will be tying in above this. In the diagram I put a cleanout in the vanity instead of the end-of-run in the basement because I may someday finish the basement.

I am in NJ and under UPC. Please see attached images.

A few questions;
1. Will this pass UPC?
2. Is a 3" cleanout required?
3. any suggestions on a better layout?

Thanks for your time!
 

Attachments

  • halfbath-topview.JPG
    halfbath-topview.JPG
    13.5 KB · Views: 1,304
  • halfbathsideview.JPG
    halfbathsideview.JPG
    45.6 KB · Views: 3,562

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Dwv

1`. It should unless the inspector has a problem with the sanitary tee beneath the toilet, AND/OR you run out of room and cannot connect the toilet flange to the tee.

2. YES.

3. Not without seeing the actual job site.
 

Zenman

New Member
Messages
58
Reaction score
1
Points
0
Location
New Jersey
Thanks for the replies...

Regarding the sanitary tee, actually I was thinking of using a wye, but now see that it wont fit vertically. What does this situation call for, a tee or a wye?

The floor joists are 2x10s, 16 inches on center and the toilet flange is all the way to one side of the joist, so I just might have enough room to roll the wye (or tee) on its side and connect the flange that way.

So I guess my question is, should I use a wye or tee?
 

Zenman

New Member
Messages
58
Reaction score
1
Points
0
Location
New Jersey
I'm surprised at the replies suggesting to use a Tee on its back. I remember reading that a Tee should never be on its back unless it was a dry vent. (I guess there are exceptions to any rule.) A couple more questions if you don't mind...

1. Why a Tee as opposed to a Wye in this situation?

2. Would using a Wye not meet UPC code?

Thanks!
 

Shacko

Master Plumber-Gas Fitter
Messages
559
Reaction score
1
Points
0
Location
Rosedale, Md
You answered your own question about the tee, more room, a wye or combine fitting will meet code, the use of tees gets a little tricky depending on the application.
 

Zenman

New Member
Messages
58
Reaction score
1
Points
0
Location
New Jersey
Ok thanks. :) If I can fit a Wye, then I will use that, otherwise I will use the Tee. I'll dry fit and test to see if it will fit it. Like I said previously, I think I can roll the Wye on its side and then have the toilet flange come in via a closet 90 elbow. Thanks for everyones time and expertise!
 