Molo Member Messages 922 Reaction score 2 Points 18 Location Cold New York May 10, 2009 #1 Hi, There are two 40 gallon tanks on one vent. Is this acceptable? Thanks for any replies
Kingsotall Plunger/TurdPuncher Messages 1,238 Reaction score 1 Points 0 Location Flagstaff, AZ May 11, 2009 #2 What size is the vent¿
Molo Member Messages 922 Reaction score 2 Points 18 Location Cold New York May 11, 2009 #3 The standard size that comes off of most water tanks.
hj Master Plumber Messages 33,613 Reaction score 1,057 Points 113 Location Cave Creek, Arizona Website www.terrylove.com May 11, 2009 #4 vent ONLY if it is large enough for both of them. Two 3" heater vents into a 3" flue would NOT be acceptable.
vent ONLY if it is large enough for both of them. Two 3" heater vents into a 3" flue would NOT be acceptable.
Kingsotall Plunger/TurdPuncher Messages 1,238 Reaction score 1 Points 0 Location Flagstaff, AZ May 11, 2009 #5 molo said: The standard size that comes off of most water tanks. Click to expand... Was talking about the flue going into the ceiling.
molo said: The standard size that comes off of most water tanks. Click to expand... Was talking about the flue going into the ceiling.
Molo Member Messages 922 Reaction score 2 Points 18 Location Cold New York May 11, 2009 #6 Sorry, Yes it's all 3"
Molo Member Messages 922 Reaction score 2 Points 18 Location Cold New York May 11, 2009 #7 I sized the vent with a local plumbing/heating guy and it looks like 5" after they connect. Thanks for the help.
I sized the vent with a local plumbing/heating guy and it looks like 5" after they connect. Thanks for the help.