View Full Version : Using plastic/vinyl 1/4" for hot water to humidifier
Fubar411
03-01-2009, 07:30 AM
Ok, I think I may have figured it out. After twice having my basement sprayed with hot water, are you not supposed to use vinyl for hot water?
I installed a whole house humidifier a couple weeks ago, and everything was ok when it wasn't running much (we had a couple weeks of warm, high humid air). But now that it is cold out, the humidifier is running more and more. I figure the vinyl hose is warming up (I used the hot line) and then it pops out of the fitting. I'm using the right stuff, where you put a sleeve in the tube then tighten it down. The fitting stays on fine with no leaks...but twice I've had to clean up a huge mess when it pulls out.
I'm thinking I need to switch to copper, which is fine. Just need to know if that is my problem.
1. you do not mention using the brass insert sleeve inside the tubing, and if not, that means the tubing can soften and slide out of the fitting. WITH the ferrule the tubing can soften, but it cannot "shrink" because the ferrule is keeping it to size.
2. Are you using the "milky" white or the clear tubing? You cannot use the clear stuff for any pressure application, hot or cold.
nhmaster
03-01-2009, 08:22 AM
I woudn't use that cheap vinyl crap for anything cept beating the cat.:eek:
SewerRatz
03-01-2009, 09:47 AM
When ever I get hired to hook up ice makers and humidifiers, i always install a angle valve (saddle tees are against Illinois code) and use copper supply pipe.
Fubar411
03-01-2009, 10:58 AM
No saddle valve here, I've hated those things most my life...I'm starting to have the same feeling towards this vinyl tubing. I used a 3/4x3/4x1/2 T and then put in a 1/2" ball shut off. I know, overkill and probably screams DIY, but I don't like the normal shut offs that I've had to replace over the years either.
Yes, it is the milky plastic stuff. Is it not for use on hot? I have some of the copper left over from when there was an icemaker hooked up. I'm guessing I'll just use compression nuts on it.
SteveW
03-01-2009, 12:11 PM
Good plan to go with copper.
In addition to the bursting risk, there are too many hot things around a furnace to use meltable tubing.
You are using the right tubing, but have not said if you used the insert sleeve.
Fubar411
03-01-2009, 02:33 PM
I am using the inner sleve. It worked fine for maybe three weeks, but once the furnace was on fairly regularly, I think the hot water deformed the tubing enough to break free.
jadnashua
03-01-2009, 05:20 PM
I wouldn't use hot water into the humidifier unless specifically called for by the manufacturer.
Fubar411
03-01-2009, 07:10 PM
Ok, did it with copper and much better results than before. After reading some of the problems with Pex and repiping a house that had cpvc, I am a convert to this new copper piping fad.
SteveW
03-01-2009, 07:27 PM
Aprilaire, and some others, do recommend hot water for their flow-through humidifiers especially if used with a heat pump, since the warm air coming off the a-coil in a heat pump is not as warm as from a regular furnace. Using hot water makes for a little better evaporation from the media pad.
Gary Swart
03-01-2009, 08:06 PM
I have no knowledge of humidifiers, but I would never use a saddle valve and plastic tubing for anything. That crap is sold to DIYers to install ice makers and anything else that uses just a small amount of water, and people buy it because it looks so simple and no one mentions the fact that they tend to fail fairly quickly. It costs just a few buck more to use a tee, ball valve and adapters, and a coil of 1/4" copper tubing to make a permanent installation.
nhmaster
03-02-2009, 06:37 AM
saddle valves don't meet code and should never be used. A customer of ours had saddle valve blow off and water damaged about 20 grand worth of antiques stored in the basement area. Their insurance refused to pay.