AC Cable to NM (ROMEX®)

Users who are viewing this thread

mrhoades

New Member
Messages
8
Reaction score
0
Points
0
My house built in the late 40's uses old BX cable (no bonding strip) and an 1980's renovation using AC cable w/the bonding strip. I would like to begin finishing my basement.... Am I allowed to add new circuits using NM (ROMEX®). If so how do I ground inside the fuse box?
 
Last edited by a moderator:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
If an armored cable is being used I hope that there is a metal box also. The equipment grounding conductor of the NM cable bonds to this metal box
 

RayP

Vocational Instructor
Messages
13
Reaction score
0
Points
0
Location
Syracuse NY
Yes

You can as long as you have the correct ground. Easy way to do this is replace your box and grounding electrode, and also the service cable. This sounds hard but is not. You can pay to have an electrician do it for $500-$1000, where I am (upstate NY). Homeowners can do it themselves here, after claiming to have the skill. You then need to have it inspected before cut in by the utility company.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
You can as long as you have the correct ground. Easy way to do this is replace your box and grounding electrode, and also the service cable. This sounds hard but is not. You can pay to have an electrician do it for $500-$1000, where I am (upstate NY). Homeowners can do it themselves here, after claiming to have the skill. You then need to have it inspected before cut in by the utility company.

Why would you need to do all this just to convert from AC to MN?
 

GabeS

Remodel Contractor
Messages
293
Reaction score
0
Points
0
Location
Brooklyn NY
The old armored cable without the bonding strip: That stuff is grounded. When I test that wiring it shows ground.

Is it not allowed to connect new bx to the old?
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
The old armored cable without the bonding strip: That stuff is grounded. When I test that wiring it shows ground.

Is it not allowed to connect new bx to the old?

If the AC cable does not contain a bonding strip then you cannot use the jacket as an equipment ground, nor extend those circuits with NM. Just start installing new circuits with NM back to the panel. Which I believe was your orginal question to begin with, Inside the panel the grounds and neutral conductors tie to the same bus.
 
Last edited:

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
You can as long as you have the correct ground. Easy way to do this is replace your box and grounding electrode, and also the service cable. This sounds hard but is not. You can pay to have an electrician do it for $500-$1000, where I am (upstate NY). Homeowners can do it themselves here, after claiming to have the skill. You then need to have it inspected before cut in by the utility company.

I dont know why your suggesting any of that...
 