I have a PowerMax+ Security system that has a maximum output of 550mA at 12dc volts for a remote siren. I have a large 6v bell that requires .5 A.dc
I hooked the bell up and tried it for about 5 seconds and it is really loud.
I am conserned that damage may be done to either the bell or the security system, main consern is security system.
I guess what I am asking is 550mA considerably less then .5 amp. I am also aware that I am using a 6volt bell with a 12volt source.
jimbo
01-26-2009, 04:24 PM
1 amp is 1000 milliamp. 550 ma is 0.55 amps
CarlH
01-26-2009, 04:36 PM
Hooking up that 6V bell to a 12V power supply will roughly double the current draw (Amps) of the bell. That would be about 1000 mA or 1 A for the bell running off of the 12V supply. I would not hook that bell up to that system or you may either blow any over current protection on the power supply or damage the power supply.
Giles
01-26-2009, 05:48 PM
THANKS to both of you for the quick answers. I felt that this was the situation and that is why I only ran the bell for 4 or 5 seconds. Even that could have caused problems! I guess I could use a relay and separate power source but that is a thought for later. I have a 12v external siren but the bell is, of course, much louder.
Thatguy
01-27-2009, 10:16 AM
Assume the 12v supply goes to 14v with no load. This gives an internal impedance of (14-12)/0.55 = 3.6 Ω.
Your load is 6/0.5 = 12 Ω at 6(0.5) = 3W, rated power.
Your bell saw 14(12)/(12+3.6)= 11v @ 14/(12+3.6) = 0.9A for a power of ~10W.
You might have shortened the life of your bell.
Use a series dropping resistor.
You want a half amp, so 14/R = 0.5, so R = 28 Ω; the bell uses 12 Ω so you need another 28-12=16 Ω, with a power rating of 2x(16(0.5²))= 8w.
Believe it or not, a 75w incand. household lamp will do pretty well for this resistor. It won't light and probably won't be warm. If the measured bell voltage is less than 6 then use a larger bulb.