I have just dug my trench and am proposing the following layout "attached the top view" of my DWV. Can experts please advise!!! Thx
Redwood
01-25-2009, 07:48 AM
I see a few problems...
S-trap for shower.
AAV venting laundry standpipe and shower.
Shower on the same 2" line as the laundry standpipe...
I would suggest revisiting the drawing board.
Are you having this permitted and inspected?
C NUMB
01-25-2009, 07:50 AM
Good job on the layout, but I would use a 3x2 combo for the vent on the water closet and keep 3" up to the wye for shower and laundry connection and 3" to the base of the laundry stack. Also keep 2" for wm drain. Have done similar connections down my way way and if you can re-vent the laundry stack instead of the aav it would be more advisable.
http://www.city-data.com/forum/members/esplumbing-378252-albums-misc-shots-pic21706-01-25-2009-10-04-35am.jpg
gsici
01-25-2009, 08:44 AM
Thx Redwood. I made a mistake in stating S Trap it is actually a P Trap without the clean-out. I have changed my mind with the AAV and decided to vent straight up and run to a nearby vent.
Why is 2" not enough to run a sink and shower?
I read it as "lavatory", not "laundry", and 2" is adequate, if not preferable, for that usage. Where does the toilet vent go once it gets to the basement ceiling? IF there is a vent to connect to, why would you possibly cause yourself future problems by not connecting the lavatory/shower vent to it?
gsici
01-25-2009, 08:49 AM
Thx C numb. I did have a 3X2 vent for my closet drain (unless I misunderstood?) I will definetly remove the AAV.
Also is 1/8th the same as 45 degrees?
C NUMB
01-25-2009, 08:51 AM
My bad, I thought it said laundry. 2" would be fine for sink and shower.
Yes on the 45
gsici
01-25-2009, 09:10 AM
HJ
Thank You. I am assuming that you are saying my original design with 2" will accommodate shower and sink.
The toilet vent gets connected to a 11/2" vent straight above it which vents the powder room above(mainfloor) and then continues to go up and eventually through the roof.
The reason I was going to use AAV on the shower sink was that the vent although only 7 ft (as th crow flies) to the toilet vent, I would go aginst the joists and did not want to build a bulkhead. The only way for me to tap into it would be an 8ft run parallel to the joist into a nearby bulkhead then back across the joists 7ft and tap into then. AAV or this????
Redwood
01-25-2009, 09:16 AM
My bad on reading laundry.
Damn small print... I guess the eyes are shot!
Okay lav wet venting the shower is fine.
Good idea on reventing the lav instead of using an AAV.
nhmaster
01-25-2009, 09:18 AM
You can wet vent the entire bath group through the lav. The toilet doesn't need a vent.
gsici
01-25-2009, 09:30 AM
Thx NH Master.
This is true even with the long run?
Just so I understand......Remove the 3x3x2" next to the closet flange?
nhmaster
01-25-2009, 09:46 AM
IPC will let you run "unlimited" distance from toilet to vent. All the other fixtures have to be within limits depending on pipe size.
gsici
01-25-2009, 10:17 AM
So back to my sink and toilet. Should I use the AAV or is the run of roughly 15 feet okay?
C NUMB
01-25-2009, 10:35 AM
Updated drawing for you
http://terrylove.com/forums/picture.php?albumid=11&pictureid=84
Good luck with the project
gsici
01-25-2009, 12:46 PM
C Numb. Thx but nothing attached
C NUMB
01-25-2009, 01:10 PM
I'll try this
http://www.city-data.com/forum/members/esplumbing-378252-albums-misc-shots-pic21722-01-25-2009-12-52-34pm.jpg
nhmaster
01-25-2009, 07:13 PM
Perfect......:)
gsici
02-15-2009, 12:18 PM
Thx for all your help. I have finished the DWV and now am moving into the next steps and have a few questions.
1) I have picked up a steam generator and the steam outlet valve is a metal 3/4" threaded male fitting. The instructions call for a 3/4" "steam copper piping". Needless to say my friends at Home Depot have no clue what this is? Is it the standard 3/4" water supply copper or am I into black pipe?
2) I am installing a shower head and am planning also using a handheld shower head. Can I buy the standard shower and tub diverter fixture and use the tub portion to feed my handheld shower head?
You use copper tubing. Only use the tub port for a handheld if you want water coming from the shower all the time, even when using the handheld.
gsici
02-15-2009, 12:32 PM
Thx HJ, but why would the water come out of both. Right now I can divert to either my tub or shower head. Why would this not be the same?
gsici
02-15-2009, 12:38 PM
Home Depot carries Type L and Type M 3/4" copper tubing. Is there a preference? I believe one is for gas!!