View Full Version : Tankless in an unconditioned NJ attic
Noth Jersey
01-21-2009, 06:44 AM
Folks,
Has anyone performed a tankless attic install in the Tri-state area? I currently have a commercial Rheem indoor tankless unit. One of the call center folks, after consulting with a tech for like five minutes, told me the freeze protection mechanism should make the attic install a viable option. Despite what the call center says, I'm under the impression that the freeze protection mechanism is a measure of last resort. I'm not sure it's made to operate on a continuous basis from late December through early March. My goal is to have no water heater in my basement. I'm not interested in saving the planet by consuming less energy or something. My CFLs are supposed to do that. :D What is a good solution to protect the Rheem unit from freezing temperatures?
Thanks,
Ben
Ladiesman271
01-21-2009, 06:50 AM
The solution is not to expose the unit to freezing temperatures.
Read the manual. Everything is explained in it.
Noth Jersey
01-21-2009, 06:57 AM
Right, but do you have any experience expanding a home's envelope to encompass the portion of the attic with the water heater without compromising architectural appeal of a home, e.g., building an enclosure in the attic with a louvered vent to the living space?
Noth Jersey
01-21-2009, 06:59 AM
I really wish I had another "r" in my handle
gregsauls
01-21-2009, 07:26 AM
Folks,
Thanks,
Ben
I'm not familiar with the Rheem units, but other brands do have models that are "externally" mountable and as such their freeze protection is 1st line defense. I would follow Rheem's suggestions.
Noth Jersey
01-21-2009, 08:21 AM
I'm not sure the call center folks really know. "We haven't ever heard of any problems with an attic installation." and "I'm not really sure what would happen if the heater were exposed to freezing temperatures." Anyway, I'm not sure that my house is large enough at this point to internally supply the needed volume of air for combustion specified in the manual:
A confined space is one having a volume
of less than 50 cubic feet (1.4 m3) per
1000 Btuh (0.3 kw) of the aggregate input
of all appliances within that space.
My main floor is 22x29 with eight-foot ceilings and the walkout basement on the same footprint has 7 foot ceilings. That puts me very close to the 10,000 cubic feet required to feed this baby. That's assuming that all my rooms are communicated with sufficiently large vents. So my house is on the threshold of being a "confined space."
jimbo
01-21-2009, 08:23 AM
I think the units that are outdoor rated, but you still have to protect the pipes.
It would be a simple matter to open a vent through the ceiling, and create a small "room" above, for the WH. But I think the heating cost to do so would be large.
Noth Jersey
01-21-2009, 08:58 AM
It's an indoor model, but I think that has to do more with the absence of a vent than its resistance to freezing. The manual says both the outdoor and indoor units need to be protected from freezing. I planned on foam insulation for the pipes. If I go the enclosure route, the box would be very well insulated. What's your thought on the combustion issue? Do I need to worry about having 10,000 continuous cubic feet of space? If you have eight-foot ceilings, that's 1250 square feet that must be open. I mean, I don't have to remove all the doors in my house, do I? Beads are pretty cool, but my wife likes a solid door on the bathroom for some reason.
It's an indoor model, but I think that has to do more with the absence of a vent than its resistance to freezing. The manual says both the outdoor and indoor units need to be protected from freezing. I planned on foam insulation for the pipes. If I go the enclosure route, the box would be very well insulated. What's your thought on the combustion issue? Do I need to worry about having 10,000 continuous cubic feet of space? If you have eight-foot ceilings, that's 1250 square feet that most be open. I mean, I don't have to remove all the doors in my house, do I? Beads are pretty cool, but my wife likes a solid door on the bathroom for some reason.
Get a direct vent tankless water heater and you don't have to worry about having enough combustion air from the room. With direct vent, all combustion air is taken from outside. If you don't want to use direct vent, and you are in a confined space, then you will have to provide 2 openings to the space that the water heater is located. I'm in California, so I'm not sure what your code says in New Jersey.
gardner
01-21-2009, 09:20 AM
A leak in your basement is one thing. A leak in your attic is something totally different. Why tempt fate? The internal freeze protection is electric -- a 4 hour power outage could destroy your home. And the freeze protection does not protect the plumbing, so you have to figure out how to protect that separately.
Noth Jersey
01-21-2009, 09:52 AM
Yeah, the enclosure thing sounds like the way to go. I'll have vent issues if I try to locate the water heater next to the well pump in the basement utility room (windows, porches, sidewalks, and doors). The existing water heater is right in the middle of the space where my dedicated home theater is being built.
Noth Jersey
01-21-2009, 09:54 AM
I really wish I had purchased a direct vent model.
Gary Swart
01-21-2009, 12:01 PM
Before it's over, you're going to wish you had not gone tankless.
Noth Jersey
01-21-2009, 01:25 PM
Yeah, it seemed like a practical solution to fill a 200 gallon garden tub and to get the tank out of my home theater.
gregsauls
01-21-2009, 02:20 PM
Don't let the anti-tankless gang talk you down. You have the right idea, just the wrong implementation. Put that indoor unit in an area that shouldn't freeze and all will be well. I bet there is somewhere in that basement this unit can go????
Ladiesman271
01-21-2009, 03:39 PM
Yup, I went tankless to help out with my HT layout. My HT layout is more of a multi purpose room, so I added the washer and dryer hidden at the rear of the HT room. I also added a direct vent gas fireplace for heat for that basement room. I did not have enough room for a clean HT layout, the gas fireplace and a tank type water heater, so I went with a tankless water heater B vented via existing chimney.
No problems with the tankless even with 40 degree incoming water temperature.
Noth Jersey
01-21-2009, 05:37 PM
You know, I could locate the tank elsewhere, but I'd be putting the unit about 20 feet further from the kitchen and the location of the new master suite. The run from the well pump would also be lengthened about 20 feet. I would have to run the 1" Wirsbo PEX along the rim joist to avoid punching 30 holes round trip in my floor joists. I guess I'd have to run the whole bundle of 1/2" along the rim joist as well. I'm just want to be sure I can supply enough volume for my Kohler River Bath and everything else.
master plumber mark
01-21-2009, 06:37 PM
If your attic is not heated,, it will eventually freeze solid....
so why not just put
that tankless heater outside on the back porch so when it
finally freezes and explodes it wont flood the whole house????
it might as well be outside ......
those peopel that give the advice on these things
will tell you ahything to get you to buy one
you are on a well, so you got to have a water conditioner
where are you going to put the water conditioner??
master plumber mark
01-21-2009, 06:43 PM
Yup, I went tankless to help out with my HT layout. I did not have enough room for a clean HT layout, the gas fireplace and a tank type water heater, so I went with a tankless water heater B vented via existing chimney.
I dont want to tell you what to do, but what I have read
about all the tankless is that they must have a dedicated chimmney usually run out of the proper SS materials...
I also was going to install one into my brick and tile chimmney and save me tons of trouble,,,,
but was told by Takagi that was a very bad no-no...
I might burn down the house due extremely to high temps...
did you b-vent completely through an existing old chimmney, or did
you jsut dump the fumes into an old chimmney
but you ought to check this out with whoever you bought that from
Noth Jersey
01-21-2009, 07:24 PM
so why not just put
I really wanted to colocate the heater with the water softener and the blasted flow restricting sediment filter, but they sit in the corner of the house with the main entry door, porch, windows on both walls, and sidewalks below (this is a largely above-grade walk-out basement). If I ran the vent along the rim joist, I'm not sure I could maintain clearance from combustible materials. The twenty-foot run would also require a five-inch drop for condensate drainage.
So the whole freeze protection to -30 is inaccurate? The advice I got was post-purchase from the Rheem folks. They seemed pretty convinced that it would operate OK in the attic. Macplumb 777 told me about a freeze kit from Paloma, which apparently owns Rheem. I don't like the sound of having the coil freeze solid.
gregsauls
01-21-2009, 07:54 PM
FWIW, my tankless is about 40 feet from our master bath. In comparision between our old tank setup and our tankless, it takes about 8 seconds longer to get hot water now to get to the shower.... No biggy. You won't have a problem filling that 200 gal tub that's for sure!
On another note, it would scare the crap out of me to have pipes to tankless in the attic that could freeze. Talk about a making a mess of the house. But maybe they do that up north and don't think twice.
jadnashua
01-21-2009, 08:53 PM
While the anti-freeze stuff IN the tankless might prevent it from bursting internally, it won't do much of anything to the pipes coming and going from it. And, as noted, if you have a power outage, all bets are off. Keep in mind that all of that combustion air is being pulled through cracks in your house, bringing in outside air (and if it can't get enough, creating CO). This negative pressure will also affect things like a gas stove, dryer, fireplace, etc. This will mean more air you have to heat, killing any savings on the tankless. In the winter, what does it say about gpm flow rates? The things often adjust the flow based on the incoming water temperature. So, to get it warm enough, you might only get 3 gpm, so to fill your 200 gallon tub, would take maybe over an hour. In that time, what is in there is cooling off, so you'd be tempted to start with it much hotter, wasting more energy.
So, really, what kind of flow rate and outlet temperature can you get with say 40-degree inlet temperature water? Are you willing to wait an hour to fill the tub in the winter? It should go much faster in the summer, but maybe not depending on the depth of the well and the size of the bladder storage tank. The solution, if you stay with tankless is to maybe use two units in series, or get a much bigger unit, which would have even more combustion air makeup problems (unless you go with direct vent). Is your gas line big enough, too? A good 3/4" valve to your tub could draw 14 gallons/minute and fill the tub quickly IF there's enough flow. You sure your pump can keep up and the well produce enough? That's a pretty big tub!
Ladiesman271
01-21-2009, 11:56 PM
Takagi specifies type 3 venting. The Takagi units have fan assisted exhaust. You can't vent those units into a chimney per the gas code book. That so called "high temperature" claim means nothing to me.
I have an older atmospheric vented ELM Aquastar that only requires a single wall gas vent into a gas vent or chimney. B vent is preferred over single wall in a cold climate (gas code). My unit is 5" B vented to the 8 x 12 (?) clay tile liner of the masonry chimney. This conforms to the 7 X rule.
master plumber mark
01-22-2009, 05:14 AM
that is about what I had palnned, and for me it would
have been almost a direct dump into the 8x12 tile liner...
I was told that Takagi frowns on that....becasue it blasts out of the unit almost like a jet engine...
So if they tell me it might burn my house down,
I generally take notice..
I will have to do some more ivestigation....
This sort of makes me wonder how many people
have thrown away the instruction manuels and just
rigged up these things to what loooks like will work..???.
Ladiesman271
01-22-2009, 06:44 AM
I think the issue is moisture, not excess heat. You ever hear the story about the exploding tank type water heater? How about the exploding house?
I have read the 1996 Gas Code Handbook, and what it pretty much says in Section 11 is that fan assisted units can not vent into a masonry chimney. You need to have all old type draft hood units with no fan assist on any unit connected to the vent. There are various tables in that vent section.
Anyway, the handbook also states:
Exception: The installation of vents serving listed appliances shall be permitted in accordance with the manufacturer's instructions and the terms of the listing.
The way I understand the gas code, since the Takagi units (all fan assisted) require the type 3 vent that is what has to be used. That means follow the Takagi instruction manual.
If my present tankless ever goes bad and is not repairable, there is no current B vent unit around that has a thermostatic water temperature control. I will be forced to do a chimney reline or something else if I need to replace my present unit.
I still have my 50 year old original hot air furnace that I am looking to replace in the near term. The plumbing inspector said that as long as the water heater drafts properly after the old FHA heater is removed from the shared vent, I only have to conform to the 7 times rule for the water heater.
Yep, the issue with the newer higher efficiency forced-draft units is condensation. With less dilution air they get better controlled higher combustion-efficiency, but less dilution air also means higher CO2 concentration, which lowers the exhaust's dew point. That, combined with the lower exhaust temp due to the higher-efficiency heat exchanger, stack condensation is all but guaranteed (even in side vented units.)
The older atmospheric drafted units like the E.L.M. never got much above 80% combustion efficiency, whereas the newer ones are all in the mid- or even high 80s. The new ones are in many respects more akin to low-mass modulating boilers than the old-school tankless heaters.
tourne
01-26-2009, 10:15 PM
I don't think these things are meant to be installed outdoors in a freezing climate. Takagi says that their freeze protection is only good to 5 degrees F. Your going to be running a lot of electricity to keep that thing from freezing all winter long.
Noth Jersey
01-26-2009, 11:09 PM
You're right, I think most of the outdoor models still need protection from freezing temperatures. The only basic difference between my indoor model and the outdoor model is the vent. I talked to Rheem and several techs told me that an attic install would be OK as long as my vent is sufficiently long. The inline condensate drain seems like a bad idea, especially if the heater will be in close proximity to the termination. I'm going to do a short offset with an elbow condensate drain to avoid freezing.I'm going to place the pex under tented insulation in the attic. I've also considered putting a small electric heater in a vented enclosure in the attic.
jadnashua
01-27-2009, 04:06 PM
It's my understanding that you don't see a lot of condensation until the efficiency gets a little higher. My boiler (obviously not the same as a tankless), condenses even in the summer when it's 90-degrees out (it's at about 95%). My old boiler was 88%, and there'd sometimes be drips out the exhaust vent (the horizontal section had to have a downward pitch to ensure it didn't fall back into the burner). It was hot enough to ensure it couldn't condense for at least a few feet, and you had to turn from vertical to horizontal before that.
master plumber mark
01-27-2009, 07:02 PM
[quote=Noth Jersey;181255]You're right, I think most of the outdoor models still need protection from freezing temperatures.
I hope that you dont find out the hard way about these things...
the outside units that are menat to be put outside are meant for Arizona, and florida.. NOT NEW JERSEY
I will be going to a meeting with the "expert" on thursday, the owner of the biggest supply house in our state. is having a seminar about plumbing issues
that we all face today... sells only about 50 Takagi units a month...
going to see if I can shake him down for a decent Takagi unit... and I am going to talk to them about
the issue of installing these things directly into the chimmney...
and I am going to find out wether its condensation or high temperatures that they are worried about...
Noth Jersey
04-28-2009, 07:49 PM
*UPDATE*
Well, the freeze kit thing is not available for any new models.
At any rate, I just called Rheem again and they assured me that the water heater would survive -30 amibient temperatures. They said the only real concern is having a vent that is sufficiently long. They recommended a cold-weather vent kit with a damper-style end cap.
master plumber mark
04-28-2009, 08:08 PM
*UPDATE*
I dont think I would trust anything that Rheem says.
never trust a Techey that teaches theory.....
yes, -30 that is pretty damn cold, but it dont take that to freeze pipes
you had better be installing that unit with some sort of drain pan under it. Something Like a washing maching pan with a drain to the outside...
....just in case those Rheem techs are wrong....
Also, I dont understand how the water lines going to and from this unit in that -30 temp area attic in New Jersey are supposed to keep from freezing and flooding your home either...
are they telling you to run heat tape on all the lines
all the way to the unit???
and if the unit sits without comming on for a whole day
in those harsh conditions, wont that coil get a little frosty??
is their some sort of fail-safe on this ??
Being installed the attic of your home,
I would be very hesitant about this....
Noth Jersey
04-28-2009, 08:32 PM
Yeah, the attic won't be hitting -30 here. -15 would be a record setting day. We don't go negative very often. The average low during the coldest part of the year is 14.
At any rate, I'll be running the 1" pex underneath the insulation. The only exposed area will be the 18" portion up to the water heater. Maybe I'll just run the heat tape for the last few feet. I probably will put a drain pan under the unit. The problem with putting the unit in my basement is supplying air for combustion. 199k btus requires a little more volume than we have down there.
master plumber mark
04-29-2009, 05:19 AM
[quote=Noth Jersey;198641 The problem with putting the unit in my basement is supplying air for combustion. 199k btus requires a little more volume than we have down there.[/quote]
if you can put it in your basement,
that is where it would be wise to do it...
getting combustion air to a applinace is as easy as
just putting in a dryer vent hose to
the outside....
someday over the next decade it will certainly freeze
up in the attic and its just a matter ot when..
Noth Jersey
04-29-2009, 07:27 AM
the outside....
What do you think about extending the house envelope to the attic, i.e., removing insulation between the ceiling and building an enclosure around the heater? I would have to put in a fairly large louvered vent in the door. I guess I could always put in a couple of thermostatic outlets for heat tape and a space heater.
jadnashua
04-29-2009, 09:04 AM
There are all sorts of fire code and structural issues with moving something like this into the attic and opening up the space. At least a tankless won't weigh as much as a tank would up there - most ceiling joists aren't designed for that kind of point load of a tank.
Some of these things can be installed in small spaces like a closet...is there one near the master bath that could be usurpted for that use? You'd still have the makeup air problem, but that may be doable.
A 200kbtu/h burner needs much more than a dryer hose for combustion air unless it a sealed-combustion setup. Backdrafting or lean operation due to wind-driven and exhaust fan pressure differentials are real possibilities (even in forced-draft models.) Good luck passing inspection if you're just plopping in a dryer hose into the space. (Good luck with getting it INSURED too.) 200kbtu/h is more burner than many/most home heating boilers or furnaces in NJ, and needs to be treated accordingly.
Usually the freeze protection on these suckers relies on having reliable power. If an ice storm took down all the lines an you're out of power for a few days in winter (as happened to me this past December), if the unit is outside the thermal envelope of the building you're basically screwed. (Which DIDN'T happen to me. My HW heater lives in an insulated conditioned basement, it never got below 40F even on nights when it was 10F outside.)
There are many good reasons (well beyond the scope of a hot water heater discussion) for converting attics into sealed, insulated-rafter conditioned or semi-conditioned space and dispensing with attic venting. It's both easier and better than you might think. A condensed encyclopedic overview of published research lives here:
http://www.fsec.ucf.edu/en/publications/pdf/FSEC-CR-1496-05.pdf
There are also very good reasons for going with sealed-combustion water heaters & boilers, especially if you have tightened up the place a lot (or plan to.) Takagi makes sealed-combustion kits for all of their hot water heaters, and other manufacturers have models/kits that are sealed combustion as well. Backdraft preventers on the venting offers quite a bit of freeze protection from wind (assuming it's inside the thermal envelope of the building) but can only be used on forced-draft models, (which would be most models over 100kbtu/h- I'm less familiar with Rheem, but I'd be surprised if it wasn't.)
master plumber mark
04-30-2009, 04:22 PM
the last time I re-did an attic, I sort of remember it being a lot of nasty , dirty , hot and
god awful grimey work......
and you are wanting to do all this just to get your tankless unit up there...
basically you are going to increase the overall area of your home that needs to be heated , increaseing your yearly heating bill and cooling bill,
I suppose that is a good thing if you ahve been wanting to do this anyway someday...
but to go through all this work just to be able to
save a few dollars a month with your tankless water heater...???
Why not put it in the basement, and simply put in a large enough
vent to the outside of the home for air>???
anyway, enough on this topic,
you do whatever makes you happy,
ChuckS
04-30-2009, 06:54 PM
Here is the heater I have. It is rated down to -30. It has a built in heater.
http://www.tanklesswaterheaters.com/waiwelaph28ri.html
Noth Jersey
10-01-2009, 11:02 AM
The plumbing inspector said he'll probably want me to open up the attic to the conditioned portion of the house. I don't think he realized that my home will likely not provide sufficient combustion air for a 199k btu water heater. I could place the water in a basement utility room next to the water softener and the expansion tank, but boring a 5-1/2" hole for combustion would cause the same sort of freeze problem as putting the unit the attic, right?
Is a buying a direct-vent unit my only practical option at this point?
master plumber mark
10-01-2009, 04:41 PM
dryer vents are 4 inches round and no one complains about them....
you want it to be faceing downwards towards the floor... no different than many closets with
a pipe from the attic going down to the floor for air...
A 50 power vent is probably a better choice...
the bradfords are energy star rated too...
Noth Jersey
10-01-2009, 06:30 PM
I'm afraid I'd need a 150 gallon tank heater for my 215 gallon bathtub. :D I'm not even sure a tank would fit in that closet. What type of vent material would you use to draw air from the attic? PVC? Flexible aluminum vent? Rain gutters? Since this closet sits in an exterior corner directly beneath the entryway to the house, I would have to run 7 pieces of 3" round duct up an exterior wall to provide sufficient air. What would be the consequences of notching my bottom plate to that degree?
Noth Jersey
10-01-2009, 06:50 PM
Actually, I guess I would need 7 vents since it's a vertical duct, correct?
Required free area of duct:
199,000 btu/4000 btu/inē ≈ 50 inē
Area of 3" duct cross-section:
1.5ē*3.14 = 7.077 inē
Noth Jersey
10-02-2009, 02:33 PM
Nice catch! Thanks. :)
Noth Jersey
10-03-2009, 09:53 AM
How about two 8" automatic intake dampers or a single 12" hooked up to the 24v system on my water heater? Maybe I should just try to sell this unit and buy a buy direct-vent model.