I am remodeling a condo (daughter's) with a fire rated ceiling (Type X fire rated drywall hung on metal channels-sound suppression) with protruding fire sprinkler heads.

I have opened a ceiling and after studying the system, am thinking about going to QuietRock over the channel system.

The fire sprinkler estucheons. Are they removable to be able to apply new drywall? I have been told that they merely clip to the head and can be pulled down. I understand I will have to shim the overhead joists to get to the origional depth so as not having to shutdown the system and replacing the heads.

Any insight here? Thanx!

KULTULZ
10-16-2008, 10:11 AM
Found my info-

hj
10-16-2008, 05:58 PM
The fire suppression heads MUST have the proper projection, meaning exactly the same as originally, from the finished ceiling to provide the proper spray pattern.